Just wondering after doing a job today, what is samllest fuse size you would use for sockets in a kitchen if there wasnt a washer or dryer in there ?
I put a 32a mcb with 4 double sockets and a single and when all finshed i did think with the loads present surely a 25 or 20 mcb be ok. I always had drilled into me 32 for kitchen no less for years even if there is no big app.
 
I do like 6mm for cookers tho cos i always think someone will install a hob and oven at a later date and say ive put loads of hobs and oven on the cooker circuit and it been fine for years.

I do always run 2.5mm for ovens and 4/6mm for hob on rewires now just because i think it better to have them seperate
 
When will you young electricians get it through your head, MCB's are sized to protect the cable, not the dammed loads!!!

Why would you possibly want to de-rate a perfectly sound FRC, what are you going to hope to achieve, by putting a 20A MCB on a FRC then??
 
no1 said that, but theres nothing to stop you putting in a20A radial..... if the kitchen was small and no loads tied in i.e flat or something.. come on man the rings are going going going gone
 
When will you young electricians get it through your head, MCB's are sized to protect the cable, not the dammed loads!!!

Why would you possibly want to de-rate a perfectly sound FRC, what are you going to hope to achieve, by putting a 20A MCB on a FRC then??

I know the mcb is to protect the cable but isnt the cable selected based on the load.

I wouldnt derate a (FRC do you mean RFC and besides who mentioned them n e way) i would of maybe used 2.5mm instead of the 4mm
 
I'm with E54!!

The rating of your protective device MUST be more than your Design current (>IB) and at the same time less than your current carrying capacity of your cable taking into account the appropriate reference method.

The only time I derate the protective device for a general power circuit is a) if it's a radial on 2.5 cable
B) if the ring cpc is broken and cannot be repaired ( I have had a couple of occasions where the cpc's have been cut out) so I have left the ring intact and de rated the mcb to allow for the slightly higher Zs value.
 
dont think the oringinal poster wanted to add a smaller cable to the protective device... he is saying he used to just installing rings in kitchens...at 32A

wires crossed, short circuit
 
if cpcs are cut, how does that allow a fault path back if you wouldnt mind explaining , i know i missing something simple..
I'm with E54!!

The rating of your protective device MUST be more than your Design current (>IB) and at the same time less than your current carrying capacity of your cable taking into account the appropriate reference method.

The only time I derate the protective device for a general power circuit is a) if it's a radial on 2.5 cable
B) if the ring cpc is broken and cannot be repaired ( I have had a couple of occasions where the cpc's have been cut out) so I have left the ring intact and de rated the mcb to allow for the slightly higher Zs value.
 
The last time I faced this, some moronic diy'er had cut the cpc's out ( I assume they cut em too short so just chopped em out)

So I had end to end continuity on L-L and N-N and broken on cpc. So removed socket from the point that the cpc's had been chopped, re instated l&n with wagos and fitted a blanking plate.

De rate breaker to 16a so all sockets have a fault path back on either leg al be it with a higher Zs
 
why not just break the ring and turn it into 2 radials?, if you have a ring on l + n but 2 radials on cpc, where are you getting your R1+R2 from?
 
why not just break the ring and turn it into 2 radials?, if you have a ring on l + n but 2 radials on cpc, where are you getting your R1+R2 from?

Because I knew where the break was, I knew it wasn't a hazard as it wasn't current carrying and it was safer and easier to leave it intact

R1&R2 measured and recorded as per radial, offending socket removed and blanked so all remaining had continuity
 
Last edited:

Reply to Fuse size in the Australia area at ElectriciansForums.net

Similar Threads

Hi all, looking for some clarification on MCB and cable sizes I need to run for a new kitchen. Cables will run through a combination of...
Replies
0
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all. Have an issue i'd love some advice on if anyone would be so kind. Will try to be brief. Thank you!! So, have an intermittent RCD trip at...
Replies
43
Views
3K
Hi all, I recently bought a new house and I went to check the installation on my garage. There is a double socket and a fused switch (3A) which...
Replies
18
Views
2K
Hi, I'm interested in a house built around the 1980's in Northern Ireland. I took a few photos of the consumer unit etc. which is situated in the...
Replies
0
Views
683

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock