bazbazbaz

DIY
Reaction score
1
Any thoughts as to why a fused spur connected correctly would burn out and melt the unit? Surely if it is pulling too much current (which is possible as it was feeding a socket used for car charging) the 13amp fuse in the unit would have blown before it got too hot and melted.
 
This is a mix of a poor quality spur being subjected to a probable maximum load. How much power is the charger pulling.
Not really sure how much it was pulling. It was feeding a socket used for charging a bmw i3 which was set to draw maximum (as much power as it could). I (stupidly as it turned out) assumed that if it tried to draw too much, the fuse would blow before it caused any issues. But apparently not! I’ve now replaced the spur and changed the i3 to charge on minimum power.

Perhaps it’s time for a proper car charger to be installed!
 
It looks like the line terminal was not making good contact, as the terminal itself got hotter than the fuse to which it connects. It could have been as simple as a loose screw, but was probably aggravated by the heat conducted from the fuse contacts.

Runaway thermal damage is a known problem with less-than-pefect BS1363 accessories subjected to prolonged low overload. The fuse will do a very good job protecting against an overload of 30A by blowing quickly. Less so with a load of say 18A, which will cause prolonged heating. A good quality accessory installed properly will probably last the course but if there is any weakness about the fuse contacts, or the termination is not 100%, it sets off the progressive increase in resistance that leads to burnout.

Avoidance of prolonged low overload has always been a good design goal as it is hard to protect against without massively over-engineering things.
 

Reply to Fused spur burn out in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Replies
2
Views
363
A recent EICR turned up a fault: an RCD fused spur was feeding a socket and a shower pump, and neither socket or pump had continuity on the CPC...
Replies
17
Views
3K
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Replies
11
Views
3K
Afternoon All, Just pricing up a job and thought I'd pick your brains. Quick run-down, Block of Flats with an underground car park. In the...
Replies
27
Views
2K
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
579

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock