Discuss Fused Spur Query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
I need to spur off a ring main to two locations a Boiler Control and Downflow heater.
Is there anything wrong with installing one 13A fused spur unit adjacent to a socket on the ring main and running both cables out the back of it to seperate fused spur units in the appropriate locations?
the only downside i can see is that you''ll probably have a 13A fuse for the heater and thus have no discrimination with the 1st FCU .
In the end I extended the ring (customer got a free socket on the other side of the wall!) and ran two seperate spurs as the downflow heater needed a 13A fuse so discrimination would have reared its ugly head.
Reply to Fused Spur Query in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
DIY'er question: I have a singe switched fused spur above my kitchen counter, providing power to an undercounter fridge socket beneath it. The...
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Evening all, I’m looking to install an outside light as a spur from a socket on a ring main. There is already a spur from this socket supplying...
Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Hi guys, newbie posting! Does the following sound ok... Existing circuit: SOCKET on a ring -> spur to SWITCHED 3A FCU -> SWITCH -> hardwired FAN...