Hi all from an old git still learning and hoping to do 2391 some time soon,
If doing a ze on my garage cu do I do it as a zs ?
since its fed from cu in main house do I treat it just like doing a zs and then does it become a zdb ??
Thanks all ?
 
Cheers for reply ? so just do as a zs and compare to table for size and type of mcb ?
Yep correct generally you only have Ze in one place, the source of supply. The garage CU supply is effectively no different to any other final circuit so Zs.
 
It will be Zs no such thing as Zdb.
Well I never, I was about to say if you look on the generic schedule of test results sheet you will see Zdb. Just had a look and it says Zs at DB. Right again Westy.

I like trying to find times when either you are @davesparks are wrong as it's so bloody rare! :D
 
It will be Zs no such thing as Zdb.
Actually zdb is now included on the model forms of bs7671 for the minor electrical works certificate:)
[automerge]1583411352[/automerge]
Well I never, I was about to say if you look on the generic schedule of test results sheet you will see Zdb. Just had a look and it says Zs at DB. Right again Westy.

I like trying to find times when either you are @davesparks are wrong as it's so bloody rare! :D
Zdb is included on the electrical minor works certificate on the model forms of bs7671
 
Is it actually on the BS7671 model form as it crossed my mind as you posted. It isn't listed in the abbreviation section.
 
Actually zdb is now included on the model forms of bs7671 for the minor electrical works certificate:)
[automerge]1583411352[/automerge]

Zdb is included on the electrical minor works certificate on the model forms of bs7671
Get in there Ian, well done! @westward10 please check your facts before posting :D ;)
 
Hi all from an old git still learning and hoping to do 2391 some time soon,
If doing a ze on my garage cu do I do it as a zs ?
since its fed from cu in main house do I treat it just like doing a zs and then does it become a zdb ??
Thanks all ?
Z is impedance. The e stands for external, so it's the part of the earth fault loop impedance path that is external to the customer's installation. It can only ever apply to a reading taken excluding the customer's installation wiring.

Zs is earth fault loop impedance measured at any point in the customer's installation with the highest result recorded for a circuit.

As for the pedantry about terminology, BS7671 states Zs at db on the model schedule of test results, Zdb on the model minor works cert, but only mentions Ze and Zs in the table of symbols used in the standard.
So everyone is correct :D
 
It was used by a member of the IET forum years ago and just stuck .
I can't remember the name but he was a regular contributor.
 
LOL. If the model forms contain the term "Zdb" then that is in my opinion a bad thing as it has never been a term recognised by the Regulations. It is the Zs of the distribution circuit.
 
ZDB or DB isn't in the definitions , symbols or abbreviations used in the standards of BS 7671.
As far as I can see anyway.
 

Reply to Garage cu in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
800
I want to make some electrical upgrades to my detached garage. I want to update the subpanel in the detached garage, and I want to add a 240V...
Replies
3
Views
699
Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
697
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi Guys, hopefully someone will know the answer. Testing an install on a (domestic) PME system I have a garage consumer unit supplied from one of...
Replies
17
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock