Hi all,

Rewired my dads garage today for my part p assessment, i bought an enclosure and a 16amp and 6 amp mcbs for the circuits within the garage. The enclosure only had the din rail in. No earth or neutral bars. The garage is fed from a 32amp mcb from the cu in the house by 2.5 mm cable which is rcd protected. The problem i have is that i have no incommer. Ive seen the garage boards you can get with a main rcd as the incommer but my dad wants the rcd in the house so he knows it has triped if it does!

Seems silly but i feel that a 100a incomer would be too high rating wouldnt it?

Ive got an earthing block which i will fit into the cu for the cpcs of the circuits and i will do the same for the neutrals.
 
No neutral or earth bars? What make is the enclosure?

As for the 2.5 protected by a 32A??? What type of cable is it?
 
I would change the breaker for a lower rating,is it swa feeding the garage? ask yourself would you want your assesment job to be one where you have had to put something together? you can buy a 2 way garage board with a main switch and 2 cbs for about £30.
 
As rob as stated,cobbling a board together for an assessment would be not the wisest move
An assessment candidates "show jobs" are mostly done to his best installation skill,an assessor would be unimpressed by a less than top notch effort
Don't undermine your assessment this way
 
Thanks for the feedback guys!
Cable is 2.5 twin earth, and runs through the ceiling joists in the house straight into the garage.

I will also be doing a cu change in the house so will downsive there.

Think ill just get a garage enclosure like you said with the rcd in the garage!

Thanks for the help guys!
 
yep, protect that 2.5mm at 20A, if part of it's buried in a wall < 50mm without earthed metallic conduit protection, then RCBO it. then no need for RCD in garage. don't forget if there are extraneous metal parts in the garage, these will have to be bonded back to the MET. in 10mm if it's a TNC-S installation.
 
Thanks tel! No extraneous metal parts within the garage.
With an rcbo in the house though if have to remove the rcd from the garage board, if i get one because of discrimination?
Just use a main switch then yes?
Sorry guys just want it to be top notch for the assessment
 
yep, protect that 2.5mm at 20A, if part of it's buried in a wall < 50mm without earthed metallic conduit protection, then RCBO it. then no need for RCD in garage. don't forget if there are extraneous metal parts in the garage, these will have to be bonded back to the MET. in 10mm if it's a TNC-S installation.

Tel there's no pme export here or have I missed something
 
Thanks tel! No extraneous metal parts within the garage.
With an rcbo in the house though if have to remove the rcd from the garage board, if i get one because of discrimination?
Just use a main switch then yes?
Sorry guys just want it to be top notch for the assessment
. yes, you don't want RCDs in series because of discrimination. just use a D/P main switch in the garage. anything from 40A to 100A ( it's just a switch, the current rating is the max. it will stand).

@ sedgy, i assumed it was a TN system, probably PME, OP has not said as yet. but as no ecp's then it 's irrelevant anyway.
 
1 other thing. the cpc in that 2.5mm is only 1.5mm, so measure the PEFC and apply the adiabatic. you still might have to add an additional cpc.
 
Search for a thread on here about exporting PME, very handy to know.
 
Reason for me suggesting tt wasn't really to do with exposed conductive parts etc, more to do with a earth cable needing to be run aside the supply twin and earth, if bigger cpc neededm thought it'd look untidy, think op said it'd be clipped to fench. Now what about damage from uv rays? Sometimes you can ind a reg that'd stop you doing anything.
 

Reply to Garage enclosure in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
766
Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
396
Hi My main feed comes into the garage, feeds into the meter and then out to another box with a 60AMP fuse then into the house...
Replies
20
Views
3K
Guys Need some advice please. I was asked last week to investigate a burning smell in a toilet turned out it was an extract fan one of 2 The...
Replies
3
Views
683

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock