Discuss Garage Metalwork in the UK Electrical Forum area at ElectriciansForums.net

S

Spearmint

I'm in the middle of putting some lighting and socket outlets in my garage, nothing fancy just a few of each as you'd expect. I've run it in SWA ,which will be buried eventually, from the existing CU in the house on it's own circuit. Earthing arrangement is TT which reads 14.67 ohms, not bad I thought been in for 20+ years.

There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET which reads 0.54 ohms when testing against the new garage CU earth bar. So this got me thinking... it isn't extraneous as testing shows it's already connected, nor is this a separate dwelling so in effect is within the same installation.

My gut feeling is to supplementary bond it regardless due to risk of introducing a difference in potential should there be an issue with the main bond in the house, but as far as the regs are concerned???

Thoughts?
 
I'm in the middle of putting some lighting and socket outlets in my garage, nothing fancy just a few of each as you'd expect. I've run it in SWA ,which will be buried eventually, from the existing CU in the house on it's own circuit. Earthing arrangement is TT which reads 14.67 ohms, not bad I thought been in for 20+ years.

There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET which reads 0.54 ohms when testing against the new garage CU earth bar. So this got me thinking... it isn't extraneous as testing shows it's already connected, nor is this a separate dwelling so in effect is within the same installation.

My gut feeling is to supplementary bond it regardless due to risk of introducing a difference in potential should there be an issue with the main bond in the house, but as far as the regs are concerned???

Thoughts?

Is the house DB TT or have you just done this at the garage DB?
 
The test for an extraneous part must be carried out with the earthing conductor disconnected from the MET of disconnect link open.

The test you have carried out with all main bonds connected is what you would do to establish whether supplementary bonding is required or not
 
The test for an extraneous part must be carried out with the earthing conductor disconnected from the MET of disconnect link open.

The test you have carried out with all main bonds connected is what you would do to establish whether supplementary bonding is required or not
Disconnected? Surely all metallic pipework would appear extraneous if you tested against the main earthing conductor disconnected? I have quickly tested against the garage CU (only because I was in there) which returned 0M ohms... will be going back with a wander lead to test this weekend hopefully!
Do what dave said to establish if it's extraneous or not then if it requires bonding the CSA of the SWA you have installed is to small. So you will have to replace the SWA or run in a separate bond.
Thought of that already, was going to get a length of G/Y when I stopped and questioned myself whether or not this actually required bonding.
 
There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET

Why would you need to test this water pipe?/ If it's metal and has been directly buried underground to the garage it's gonna be extraneous without a shadow of a doubt. It doesn't matter a jot whether the incoming metal water pipe has been main bonded at the house, it will still need bonding at the garage to the garages EMT...
 
Why would you need to test this water pipe?/ If it's metal and has been directly buried underground to the garage it's gonna be extraneous without a shadow of a doubt. It doesn't matter a jot whether the incoming metal water pipe has been main bonded at the house, it will still need bonding at the garage to the garages EMT...

Would it though ?, if the garage is integral to the house (part of the same building).

I would probably add the extra bond if it was easy enough to do, but would it actually require it ? I would personally say not in this case.
 
Would it though ?, if the garage is integral to the house (part of the same building).

I would probably add the extra bond if it was easy enough to do, but would it actually require it ? I would personally say not in this case.


If it's an integral garage it would be one and the same equipotential zone, and the power and lighting circuits would i imagine be supplied from the house CU.
 
If it's an integral garage it would be one and the same equipotential zone, and the power and lighting circuits would i imagine be supplied from the house CU.


That is how I would treat it, the OP said it is integral, this is really no different to having a separate additional CU in any other room in the house.

I would agree if the building was separate :)
 
I'm in the middle of putting some lighting and socket outlets in my garage, nothing fancy just a few of each as you'd expect. I've run it in SWA ,which will be buried eventually, from the existing CU in the house on it's own circuit. Earthing arrangement is TT which reads 14.67 ohms, not bad I thought been in for 20+ years.

There's a cold water feed coming from the house underground and pops back up in the garage, now this is bonded as you'd expect in the house back to the MET which reads 0.54 ohms when testing against the new garage CU earth bar. So this got me thinking... it isn't extraneous as testing shows it's already connected, nor is this a separate dwelling so in effect is within the same installation.

My gut feeling is to supplementary bond it regardless due to risk of introducing a difference in potential should there be an issue with the main bond in the house, but as far as the regs are concerned???

Thoughts?

Here in bold, now as to whether it is the type of garage with a doorway into the house is another matter ;)
 
Think he's talking about something different, ...why would he need to bury a sub main cable to the garage if it was an integral garage??
 
Well this is it, how are we supposed to advise without seeing the job, or at least a clear description ?

It doesn't help that the building regs classification does not quite marry up with BS7671, it could be classed as integral or separate depending on which way you look at it, my gut feeling would have been to make my sub-main 6mm 3 core, as it is TT, or possibly even 10mm in case they ever update it to PME, especially if it is buried.
 
Well this is it, how are we supposed to advise without seeing the job, or at least a clear description ?

It doesn't help that the building regs classification does not quite marry up with BS7671, it could be classed as integral or separate depending on which way you look at it, my gut feeling would have been to make my sub-main 6mm 3 core, as it is TT, or possibly even 10mm in case they ever update it to PME, especially if it is buried.

Let's see if he comes back to clear this point up... lol!!
 
in a domestic installation with an outbuilding and TT supply I would be looking to install a submain with a cpc suitably sized to allow me to put a rod(s) in at the outbuilding which is connected back to the MET to add to the existing earth electrode(s).

If the existing Ra really is ~14ohms i'm sure it could be improved down to a very nice value with a bit more effort.
 
Think he's talking about something different, ...why would he need to bury a sub main cable to the garage if it was an integral garage??
You're correct. The garage is a separate building to the house, it's about three metres away from the main building. My use of the word dwelling was more relating to it being unoccupied, not a living space.
 

Reply to Garage Metalwork in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
Hi there, I’m a new member to the forum and felt like I could do with some additional insight into a fault I came across on a call-out at the...
Replies
6
Views
403
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K
Hi My main feed comes into the garage, feeds into the meter and then out to another box with a 60AMP fuse then into the house...
Replies
20
Views
3K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock