I'm hoping some of you guys out there on the forum can perhaps provide the benefit of your experience with the below issue:-

Currently working on a job where the garage which is approximately 25 - 30 feet away and adjacent to the house, has its power fed to it via SWA connected off the back of a 13amp double socket in the utility room. The house is a new build built in 2010 and this was installed by the builders. The owners have requested to have additional circuits installed in the garage for which an upgrade to the existing DB will be required, however be fore I get into that I wanted to ask some advice.

The SWA is terminated within the garage to a 2-way DB, protected via a double pole 30mA RCD with 2 MCB's of 6A & 16A respectively. Obviously the cables and circuits within the garage are protected by the RCD in the DB, however my concern is the SWA cable is coming off the final Ring circuit [from the socket in the utility room] and this / is not protected by RCD other than the main RCD in the main CCU via the final ring ciruit, so any fault in the SWA will cause potential probelms not just with the cable itself, but potentially with the RCD in the main CCU and that of the final ring it is fed from, not to mention possible issues with the power in the garage.

To get round this I was wondering whether one of the following options might be a better approach

  1. Connect the SWA to a seperate FSU so as to provide a level protection if a fault occured in the cable
  2. Or use an FSU that has inbuilt RCD protection, but I'm not certain an FSU of this type is available as I have never come across one
  3. Run the circuit directly back to the CCU, however this will pose a real headache as there is no easy route, if any, to the CCU at the front of the property
  4. Leave it and do nothing and hope that the SWA cable is never compromised, ending up in further faults occuring

Any ideas / thoughts will be greatly received.

Many thanks

Stuartnt
 

Reply to Garage Power fed via SWA from the back of a 13amp double socket to a DB int he Garage in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, if getting back to the CU is not an option, instead of spurring off a socket via a Sfs putting the rating down to 13a. Could you spur off the...
Replies
43
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
713
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
878
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
The garage is 17 mtrs x 15 mtrs in the UKh The house has a 100 amp supply to the house consumer unit. The garage consumer unit is fed from a...
Replies
4
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock