Hi hope everyone is doing ok?
Question please,
Garage with swa supply on 32a mcb in house , can I replace dp switch on garage cu with dp rcd as don't have space for both in garage cu, and would like to take swa supply off of house cu rcd and put onto none side of rcd in house to prevent nuisance tripping in future ?? No issues with tripping at moment just a thought
Cheers gary
 
Yes, you really should have RCD protection in the garage and a RCD-for-switch swap is the simplest option.

However, it is hard to get selectivity (formally known as discrimination, or coordination) between protective devices unless well planned. If you can get the garage supply off a non-RCD MCB and it is a protected cable (e.g. Steel Wire Armour) so no RCD protection of the sub-main is needed then a garage RCD will give you that aspect.

However, in the event of a high over-current fault the feed MCB will almost certainly trip along with the downstream (garage) one, and possibly also the 13A plug's fuse. Usually the best option for a garage supply is to split the meter tails and use a fused switch to feed the cable, however, that is most definitely not a DIY job, and the provision of a new/modified circuit of that style is covered by the Part P building regulations in England and Wales.

So you ought to be easily to change the garage CU to have an RCD incomer, but if doing more to the feed cable then you really ought to get a professional spark to do the job.
 
Yes, you really should have RCD protection in the garage and a RCD-for-switch swap is the simplest option.

However, it is hard to get selectivity (formally known as discrimination, or coordination) between protective devices unless well planned. If you can get the garage supply off a non-RCD MCB and it is a protected cable (e.g. Steel Wire Armour) so no RCD protection of the sub-main is needed then a garage RCD will give you that aspect.

However, in the event of a high over-current fault the feed MCB will almost certainly trip along with the downstream (garage) one, and possibly also the 13A plug's fuse. Usually the best option for a garage supply is to split the meter tails and use a fused switch to feed the cable, however, that is most definitely not a DIY job, and the provision of a new/modified circuit of that style is covered by the Part P building regulations in England and Wales.

So you ought to be easily to change the garage CU to have an RCD incomer, but if doing more to the feed cable then you really ought to get a professional spark to do the job.
Cheers for reply?
Situation is supply is currently swa buried under ground on a 32amp mcb in house on rcd side of board , and small board in garage with mcb's for socket outlets and separate mcb for lighting . And wanting to put on none rcd side in house and replace main switch to rcd main switch so going on what you said I assume makes sense to do what I was thinking to do that way all circuits will be rcd protected in garage and no nuisance tripping of rcd in house if was ever an issue in garage.
Thanks for your help cheers gary
 
Bear in mind that the new RCD must be of the same manufacture and spec as the garage DB, it is no longer permitted to cobble in a different make even if it fits.
 
Bear in mind that the new RCD must be of the same manufacture and spec as the garage DB, it is no longer permitted to cobble in a different make even if it fits.
Yep understood and yes it is same make as existing board so guess what I'll be doing tomorrow well for half hour at least ? thanks again did make sense just wanted it confirmed cheers , take care mate ?
 
Bear in mind that the new RCD must be of the same manufacture and spec as the garage DB, it is no longer permitted to cobble in a different make even if it fits.
Yes, forgot to mention that!

Basically the problem with CU is the bus-bar arrangements are not standard, even though the DIN mounting rail is, so if you use a device that is not recommended by the CU manufacturer it can end badly and is now a factor covered by the wiring regulations.

Now "how bad?" varies, but it is something to consider seriously.

For garage CU the whole assembly is not that expensive, but rewiring to change it is a skilled job and doing that properly means testing afterwards, and that is not in the usual DIY tool or skill range.

TL;DR check you can get matching parts first!
 
Yes, forgot to mention that!

Basically the problem with CU is the bus-bar arrangements are not standard, even though the DIN mounting rail is, so if you use a device that is not recommended by the CU manufacturer it can end badly and is now a factor covered by the wiring regulations.

Now "how bad?" varies, but it is something to consider seriously.

For garage CU the whole assembly is not that expensive, but rewiring to change it is a skilled job and doing that properly means testing afterwards, and that is not in the usual DIY tool or skill range.

TL;DR check you can get matching parts first!
Just didn't want to start changing board due to wired with conduit to out going circuits which I know not a big deal but obviously easier to just replace main switch for rcd etc,
Yes I'll be testing ie ramp test for rcd and zdb etc, thanks guys appreciated ?
 

Reply to Garage suply in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Merry Christmas to everyone, and apologies for talking work during the holidays😅 I have my first EV charger install job early in the New...
Replies
14
Views
2K
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
653
I'm obviously still new and learning about what I can and cannot do, but essentially I want to install an EVSE at my own house for an electric...
Replies
8
Views
520
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
845
I just finished a garden room supply. The customer already had a CPN garage consumer unit that the last sparks left there, brand new in box, and...
Replies
2
Views
843

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock