Discuss Garbage disposal wiring problem in the UK Electrical Forum area at ElectriciansForums.net
I bought a garbage disposal and had it installed under the sink by a plumber. When we attach it to the power, if the switch is turned on the disposal runs. When the switch is turned off, it trips the circuit breaker. I tried attaching a different switch, but it still has the problem. The clothes washer is plugged into this same circuit and works fine.
Eleton who did the wiring on the garage disposal?
Is it tripping the RCD or just the circuit breaker that protects that circuit?
If it's the RCD then first step is to megger test the waste disposal and ramp test the RCD. Both these tests need special testers so you'll need to get a sparky.
It sounds strange usually the breaker trips when turned on not off. Did he get the power from the light switch only
@Marvo it’s the 20amp breaker feeding the kitchen and what’s so strange is the breaker don’t trip till he turns off the breaker. He hasn’t replied back so I can help him, plumbers shouldn’t do electrical
It's a 30 amp breaker in the laundry room. The folks downstairs have a partial kitchen with a sink in the laundry room. That's where we are putting the garbage disposal.
I looked up RCD. Not sure if we have this. It's a 40 year old circuit box for the house.
My theory is that I may have bought a bad garbage disposal. I'm looking up what a megger test is.
our name RCD is what you would call a GLFI, or something like that. megger test is the old name for insulation resistance test, so called because you had a megger instrument ( wind up) to test.
telectrix it’s GFCI in the Us
It was done by the plumber.
@elton could you send some pictures of the wiring on the garbage disposal and light switch. Don’t bother megging it we already know that it’s going to ground and tripping the
How do you know that?
If it is (going to ground) then how come it holds until switched off?
Devon that’s what I’m trying to figure out. You and I both know that 99% of the time when it’s turned on is when the breaker trips not the other way around. I know something funky is going on and we can debate this all night or get pictures to help the OP
[automerge]1573509386[/automerge]
@elton here’s what I’m thinking is going on the plumber used a 3 way switch he has terminated the hot to the common screw, terminated the garbage disposal to the NC contacts of the switch when it’s turned on and terminated the neutral to the NO screw. When he turns it off the NO contact closes and trips the breaker
Megawatt's theory sounds good to me.
Edit: my posts still won't show unless cleared by a moderator. What's going on?
If it its a GFCI (or RCD) that is tripping, but is holding when the switch is closed, then there is no imbalance in the circuit. If a double pole switch is fitted, and one pole is opening very slightly before the other then a imbalance will be detected and the device will trip.
But until the op comes back and confirms what's involved then we can only speculate.
@Devon he stated it was on the same circuit as the refrigerator. That branch circuit is required to be installed as a dedicated circuit by the NEC and no GFCI is required. Having said that the plumber has tapped off that circuit which is not allowed. VIOLATION
I think the OP confirmed that it's the 30A MCB that's tripping.
@DPG yes he stated that a 30 amp breaker trips when he turns it off but its not the main breaker that would shut all his power off
Yeah I get that, but I was replying to an earlier post which was suggesting it may have been the GFCI tripping.
Reply to Garbage disposal wiring problem in the UK Electrical Forum area at ElectriciansForums.net
Wiring to new dishwasher causes garbage disposal to stop working. I just installed a GE dishwasher and came across a problem with the...
Hello. I am new to wiring and could use some help getting this circuit wired in the kitchen . I am trying to get the source power to the GFCI and...
Hi All, Looking for a bit of advice. Just bought a boiling water tap, with a max kw rating of 1.5. We already have a waste disposal under the...
Hi All, Would be grateful for some advice. Would like to add an additional light (Undercabinet 8W LED Batten light) to a two-way light switch...