HappyHippyDad

-
Esteemed
Arms
Reaction score
5,600
Evening everyone..

I have just undertaken an EICR and there is 6mm bonding to both water and gas at the correct points (within 600mm of entering building), however they must be joined somewhere as there is only one 6mm in the CU. I believe this would be ok if the conductor was unbroken but seeing as though it has to be broken somewhere (cant find it) I am unsure how to code it?

I would think C3?

Ps.. Its a TT.
 
If you have proved there is a joint, but the continuity reading is under 0.05 the I would go with C3 and futher investigation, as how can you be certain the correct size cable is used along the whole length of the conductor?
 
If you have proved there is a joint, but the continuity reading is under 0.05 the I would go with C3 and futher investigation, as how can you be certain the correct size cable is used along the whole length of the conductor?

Very good point! The incoming gas is one side of the kitchen door, the incoming water the other. I think it unlikely a different CSA has been used in such a small length of run, but even if it was I believe 4mm is ok for a TT, so unless they've joined it with a bit of 1mm I'm erring towards Murdoch's advice.. but... when I've finished the EICR (I'm very slow plus its a 5 bed OLD house with lots of questionable DIY electrics) I think I'll investigate a bit more anyway! :smiley2:
 
There is no reg saying it has to be continuous. Best practice says it should be! Not convinced I'd code it at all. Tin hat on.

Thanks Murdoch,

You're very thorough and do things by the book so if you say it's probably not a code then it almost defnitely isn't! :smiley2:
 
Hi HHD,
apart from PME,the main protective bonds shall be no less than half the Earthing conductor, and in any case no less than 6mm^, 544.1.1

Hi Spark68..

I was taught 6mm to be the minimum for bonding, but if you look at page 41 (table 4.4 (ii) )in the OSG it suggests that 4mm is acceptable for a TT(or even 2.5mm if mechanically protected)? There isn't a cross reference to BS7671 though!

And then underneath table 4.4(ii) there is a Note 2, it states reg 544.1.1 (i.e minimum of 6mm) - doesn't make sense!
 
I think you may be mis-reading, the table 4.4 (i) in the OSG hhd, in mine (the light green part for MPB not PME) it is minimum 6mm^, table 4.4 (ii) refers to the Earthing conductor.

Ps.just trying to help
 
Last edited:
I think you may be mis-reading, the table 4.4 (i) in the OSG hhd, in mine (the light green part for MPB not PME) it is 6mm^, table 4.4 (ii) refers to the Earthing conductor.

Ps.just trying to help

I'm not sure why I have these conversations with you Spark68, you're always right!! :redface:

It's late, I'm tired, I'm wrong!! Of course its referring to the Main Earth - I new that (He says in hindsight making himself look even more silly)... I'm going to bed!!
 
I wasn't picking a fault, it is just if you are doing EICRs then it helps to have some guidance ( at least at first), and I happened to notice you said 4mm MPB was suitable for TT, better to correct you now rather than later.

We all had to start some where, at least you ask, I had another Spark to help me when I started.

We all need help from time to time.
 
I wasn't picking a fault, it is just if you are doing EICRs then it helps to have some guidance ( at least at first), and I happened to notice you said 4mm MPB was suitable for TT, better to correct you now rather than later.

We all had to start some where, at least you ask, I had another Spark to help me when I started.

We all need help from time to time.

I should have put a smile S68! I know you wern't being picky, you were being very helpful and I value your posts. I'd much rather look a little silly but be right. Please keep correcting me.. :smile:
 
bear in mind, though that the 50% of main earthing conductor rule is based on the required csa of the MEC, as determined by use of the adiabatic. what i'm trying to say is that you migt have a 16mm MEC< but the adiabatic required only 6mm for the MEC, then 3mm is the min size for MBCs ( subject to not<6mm)
 
Bonding conductors have a minimum of 6mm even on a TT system. Let face it, on some of the TT installs we've been told about on here, the extraneous pipework will probably be providing the majority of the installations earthing provision!! ...lol!!!
 

Reply to Gas and water bonded together with a broken conductor? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I know once you see plastic entering then you don’t need to bond as it says on site guide.(enters the house plastic then it’s metal) Would I be...
Replies
14
Views
2K
Hi forum members, I hope someone can assist with my enquiry. I have been advised that to comply with BS7671 Reg 132.16 my solar and battery...
Replies
5
Views
1K
Hello everyone, I’m based in the ROI and live in a rural location. Yesterday evening my electricity supply started to switch on and off randomly...
Replies
2
Views
2K
Good Evening. I am in the process of making some slight alterations to my Utility room, and there is a Twin and Earth cable that needs...
Replies
2
Views
3K
Hello there, I’m in the process of mapping out a relatively standard S-plan system for my parents central heating and hot water system. Not sure...
Replies
10
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock