I have been ask to fit a generator on a static caravan(metal frame is earthed) in an area which has regular power cuts. The customer has a generator but it is one which is designed for camper vans or other similar vechiles.
I have fitted changeover switch and earth rod I have connected up the generator but I don't seem to be getting an earth when the generator is running I get no efli reading an only get 110v n and 104v l to earth spike but between mains power and earth spike 230v and 114ohms efli. Does anyone have any experience with campervan generators( I understand normally the vechile the generator is intended for wouldnt be connected to earth) is there any reason I would be getting an earth. Is it possible to use this generator for this application
I have fitted changeover switch and earth rod I have connected up the generator but I don't seem to be getting an earth when the generator is running I get no efli reading an only get 110v n and 104v l to earth spike but between mains power and earth spike 230v and 114ohms efli. Does anyone have any experience with campervan generators( I understand normally the vechile the generator is intended for wouldnt be connected to earth) is there any reason I would be getting an earth. Is it possible to use this generator for this application