Im not sure on this either, floating earth springs to mind, unfortunately my mind is slowly losing its memory, anyone know the score??
regards
Simon.
Genorator that is a selv supply on an extra low voltage sysytem which is electrically seperated from earth and from other systems in such a way that a single fault cannot give rise to the risk of electric shock , or the protected extra low voltage system which is not electrically seperated from earth but satisfies all the other requirements of Selv , if that makes any sense
An earth rod is advisable but not essential. A geney will usually give you a TN-S supply, but if you cant drive a rod in to reference it to earth you'll need to create a TN-C-S system so the RCD will operate under fault. It's ok to have a separated supply for a single item of equipment, ie a power tool of some desription, but not more than one. Depending on wether or not a link is already in place between N&E, you will need to fit one You will definately need to make sure that any and all exposed steelwork is equipotentially bonded. You will need the RCD as the fault current will not be high enough for ADS via a fuse or MCB by itself.
Also if you are placing an N-E link in, then it's definately advisable to place a label warning of the link somewhere easy to see.
Sorry should add, easiest way to check for floating earth is to measure voltage at gen output, if floating earth then you will see 120-0-120 at output. If not then simply 230 between L&N or E.
Also if you do need to modify the arrangement then best not to do it at the geney iself but in the plug of supply lead or at DB.
i must be having a 'blonde' episode again:confused:
can you explain 'creating the tn-c-s supply' and the linking N-E in a bit more detail for me thanks
i'm usually a bit puzzled on these
Reply to generator in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
5 single phases to one huge property. Backup generator which can take about 106 amps split between 2 phases - 1 phase will be wired through...
I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Hi, I've been asked to look at installing a generator changeover switch at a property, so that they have some level of backup in the event of...
I am installing a Victron Quattro in an island mode configuration (in the UK, the DNO is the NG). I will be adding a stand-by generator. My...