Hello for the second time today!I've been asked to install 2, 2 gang switches in a kitchen, which will switch the fixed appliances such as dishwasher etc. Now i've not used modular switches yet but from what I can make out they're pretty straight forward. My question is about integrating them into the kitchen ring, as I was planning on looping in & out much like a socket, then having the appliance wiring drop down from each switch, similar to a spur. However in order to have the switches on the ring, I'm assuming i'll have to bridge between the two individual switches inside each panel. Am I correct in this line of thinking? As always, any replies much appreciated! :) cheers
 
You can wire it as you say, although you will have to use connector blocks for the neutral, and may have to connect four CPCs into one terminal at the grid.
Another way would be to loop into each fuse with the ring line conductors.
Then connect one side of the CPC at the grid, onto the first socket, then to the next and connect the other side of the ring CPC at the second socket.
With the neutral, one side of the ring into the first socket, on to the next and the other side of the ring connected to the second socket.
 
You can wire it as you say, although you will have to use connector blocks for the neutral, and may have to connect four CPCs into one terminal at the grid.
Another way would be to loop into each fuse with the ring line conductors.
Then connect one side of the CPC at the grid, onto the first socket, then to the next and connect the other side of the ring CPC at the second socket.
With the neutral, one side of the ring into the first socket, on to the next and the other side of the ring connected to the second socket.

I think the OP has 4 grid switches (2 x 2 gang). Each 2 gang switch will have 2 separate drops to 1 gang sockets to plug appliances in.

If this is the case then his original way of wiring it up is correct, simply linking switch 1 to switch 2 in each grid.
 
Ok, I think I follow you, however I'm assuming this is based on using single pole switches. I was hoping to use double pole, meaning no connector blocks for neutral, although I guess I can't avoid the CPC block still :(
 
Like this...

2x2GangGridSwitches.jpg
 
Last edited by a moderator:
Thanks both! My original reply was actually to the SpinLondon, I got you straight away Jud. Thanks for the help. I'm working on my own at the moment, so it really helps to have people to bounce ideas around with!
 
There's no need to use fuses as each switch only supplies 1 outlet. Each switch is effectively an unfused switched spur feeding 1 outlet.
Don't know if I like the sound of that.
Normally the device used (when not a grid switch) is an FCU above the counter, with an unswitched single socket beneath the counter.
If as you say (and too be honest I can't actually think of a reason to disagree) fuses are not necessary, then there is no need for an FCU to be used above a counter, a 20A switch would be sufficient.
 
Don't know if I like the sound of that.
Normally the device used (when not a grid switch) is an FCU above the counter, with an unswitched single socket beneath the counter.
If as you say (and too be honest I can't actually think of a reason to disagree) fuses are not necessary, then there is no need for an FCU to be used above a counter, a 20A switch would be sufficient.

What is it you don't like the sound of?

There was a similar thread to this not long ago.

http://www.electriciansforums.net/e...gulations/36758-light-switches-isolators.html

FCUs feeding single socket outlets for appliances are pointless and do not comply with 536.1 because you would have 2 x 13A fuses in series (1 in the FCU and 1 in the plug top of the device) and there would be no discrimination between the 2.

536.1 states that in the event of a fault only the device that is intended to operate should do so.

I assumed the grid switches in the OP are 20A DP switches.
 
Last edited by a moderator:
However, as you quite rightly say, there is no point in having two 13A fuses in series.

The done thing is usually to install them together with a fuse.

But you don't need a fuse. There's a fuse in the plug top. :banghead:

There's no difference between this and an unfused spur feeding a single outlet (perfectly acceptable) apart from the fact it is switched.
 
Last edited by a moderator:
But you don't need a fuse. There's a fuse in the plug top. :banghead:

There's no difference between this and an unfused spur feeding a single outlet (perfectly acceptable) apart from the fact it is switched.
I know, and I quite agree.
All I'm pointing out, is that the done thing, is to either use an FCU, or a grid switch paired with a fuse.
To be honest with you, showing pictures of switches labeled with appliances doesn't actually mean much, as you can purchase FCUs with the same lables on Buy Crabtree Moulded Fused Connection Unit, Capital, Switched, Single Gang, DP, 13A, w/o Neon, /w Legend - 4827/WM.
 
I know, and I quite agree.
All I'm pointing out, is that the done thing, is to either use an FCU, or a grid switch paired with a fuse.
To be honest with you, showing pictures of switches labeled with appliances doesn't actually mean much, as you can purchase FCUs with the same lables on Buy Crabtree Moulded Fused Connection Unit, Capital, Switched, Single Gang, DP, 13A, w/o Neon, /w Legend - 4827/WM.

Those are meant for direct connection of the appliance to the FCU (no socket outlet).

IMO the only reason for using FCUs with socket outlets is when it is feeding more than 1 outlet so as not to overload the cable.
 
Last edited by a moderator:
Its the new damn thing to do now isnt it,all appliances switched from a grid,gud point bout the fuse,must admit sounds a bit odd,also r all switches rated at 32amps,mcb wud be 32amps.Maybe thats y radial circuits may b better than a ring then rated at 16/20 amps hav a gud rainy day ta ra bab
 
IMO if your going to the bother of grids above worktop Id feed to an unfused conection unit under and fit fuse module in the grid as this would save howking the appliance out if fuse goes or put the plugs in next cupboard to appliance for access
 
Last edited by a moderator:

Reply to Grid wiring in a kitchen ring in the Australia area at ElectriciansForums.net

Similar Threads

Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
as title, am looking for square edge grid switches. I rewired a little bungalow and wired it for grid switches beside double sockets in kitchen...
Replies
5
Views
604
Hello Electrical world. Looking for thoughts and opinions. Currently planning out my kitchen re-wire for new kitchen. I was originally...
Replies
13
Views
3K
Hi there I have 8 downlights in my kitchen, 6 on one switch and 2 on another (not sure why), I've replaced the downlights on the 6 and they work...
Replies
1
Views
571
I'll start by saying - I have absolutely no intention of doing any wiring or anything electrical myself. You get someone professional to do a...
Replies
8
Views
779

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock