Hi all,

I work in a nutritional powder factory and we have an automated bag filling machine that takes the bag from a stack moves it down a conveyor where it is then picked up and placed in two grippers that open the bag ready for the powder to be dispatched into it.
My question is this.....there are two plunger type switches,one on each gripper that are then wired to the plc.
Occasionally the plunger type switch will stick due to the nature of the powder and if the bag is not properly held in the gripper the powder will still be despatched because the plc thinks it is in place due to the switches being made.
How can I rectify this issue by fitting an added safety feature?
We have tried changing the switches but the problem still persists!
Thanks in advance.
 
Material dependent could you use an inductive sensor rather than a plunger to detect the gripper closed state?

Or less fail safe, twin plungers with the PLC set to raise a flag if the logic state of each differs. This would just be an alert rather than solving the issue, and not failsafe as both plungers may stick!
 
Last edited:
Try these people.
 
Thanks for the replies guys!
I did think of an inductive sensor but due to the nature of the mechanism and it's movement I don't think it would work.
The double plunger on each side though could potentially work if there is room unless you can buy a unit with a double plunger?
I'll email Keyence to see if they've come across this issue before and have any product to remedy it?
Thanks againđź‘Ť
 
Pics of switch and circuit
 

Attachments

  • IMG_20240613_164836_200.jpg
    597.4 KB · Views: 26
  • IMG_20240613_164949_635.jpg
    483.5 KB · Views: 28
  • IMG_20240613_165854_671.jpg
    231.6 KB · Views: 24
  • IMG_20240613_165906_790.jpg
    395.4 KB · Views: 25
  • IMG_20240613_171242_970.jpg
    70.8 KB · Views: 25
Is the issue, that the plunger switch does not return to the off state because it is stuck ?

If so there are a couple of ways to solve this, either by the PLC detecting the off-state (i.e. because it is not in the on-state), this can be done a number of ways depending on plc type and programmer preference but essentially the off-state resets a virtual output which needs to be made prior to a signal to close the jaws again.

Or a dual switch to detect both clamped state and un-clamped state which can be used by the plc to ensure before the jaws are clamped that the un-clamp state is detected.

Or use a different detector as previously mentioned to detect the state of the jaws.
 
Is the issue, that the plunger switch does not return to the off state because it is stuck ?

If so there are a couple of ways to solve this, either by the PLC detecting the off-state (i.e. because it is not in the on-state), this can be done a number of ways depending on plc type and programmer preference but essentially the off-state resets a virtual output which needs to be made prior to a signal to close the jaws again.

Or a dual switch to detect both clamped state and un-clamped state which can be used by the plc to ensure before the jaws are clamped that the un-clamp state is detected.

Or use a different detector as previously mentioned to detect the state of the jaws.
Yes that's right,the plunger switch remains in the on position.
I think the first option you mentioned may be the best as it will be a programming upgrade on the plc that will take away the ineffective mechanical set up that's constantly exposed to the sticky powder.
I have limited knowledge on PLC's so will have to seek advice from a third party.
Thanks for your advice and suggestions,much appreciated đź‘Ť
 
This thread hasn't been replied to for 14 days, so replying to this one may not get a response. Post a new thread instead.

Reply to Gripper sensor in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock