Hi guys.

Im from Denmark. I just signed up in here, and I have a question about how to test my ground rod.

I dont have any electrical experience, but im really trying to learn. so please bare over with me..

Well I have a cnc plasma projekt that I have problems with.

The problem Is when i turn my plasma on, It causes my cnc program to frees and error pops up. I have to restart everything, try again and same problem over and over again.
I look In some forums, and it seems like something called EMI is a huge issue on HF Plasmas (Never heard off EMI before)
It seems like other people change there wires to shielded wire, and improved there ground.

So I tough If I change my wire and make a brand new ground stick I would be over that problem. BUT NO NO!! Stil the same issue.

So now I think i maybe should test my new ground for the plasmatable. I only got a cheap multimeter, so I read how to do it easy with that.

But why do I get 0.258 Vdc when i stick new ground rod and neutral together? and -0.04 Vdc when old groundrod (2 years ond) and neutral together?

Hope you can help here.? :)
 
Last edited:
Is this a home built project or a purchased machine?
If you have purchased it, the instructions are a great place to start.
If you have built it then can you post some pictures of the electrical control panel?
 
Is this a home built project or a purchased machine?
If you have purchased it, the instructions are a great place to start.
If you have built it then can you post some pictures of the electrical control panel?

It is a purchased CNC laser, that i have build a plasma on.
 

Attachments

  • 20190729_162452.jpg
    2.8 MB · Views: 20
  • 20190729_162506.jpg
    2.6 MB · Views: 19
  • 20190729_162526.jpg
    1.2 MB · Views: 21
  • 20190729_162552.jpg
    2.7 MB · Views: 19
make sure that the ground connection for the plasma torch is kept separate from the other ground connections.


there are so many ways that the high frequency could be getting to the pc systems

you might find that physically moving the cnc control box well away from the plasma generator will help.

where you have cables feeding the plasma head, do not run them together with any servomotor cables or feedback cables.

probably better to put the cnc on one side of the base and the plasma generator on the other side, that way you separate the cables as best you can.

shielding on the cables will help but ensure that the shields are not connected to each other apart from at the relevant control panel.
all shields should be attached to ground at the control panel end of the cable.

where you have to have plasma head power running close to other cables, make the run as short as possible, try not to run them parallel to each other and if you can have a grounded metal plate separating them, even better.
 
Hi guys.

Im from Denmark. I just signed up in here, and I have a question about how to test my ground rod.

I dont have any electrical experience, but im really trying to learn. so please bare over with me..

Well I have a cnc plasma projekt that I have problems with.

The problem Is when i turn my plasma on, It causes my cnc program to frees and error pops up. I have to restart everything, try again and same problem over and over again.
I look In some forums, and it seems like something called EMI is a huge issue on HF Plasmas (Never heard off EMI before)
It seems like other people change there wires to shielded wire, and improved there ground.

So I tough If I change my wire and make a brand new ground stick I would be over that problem. BUT NO NO!! Stil the same issue.

So now I think i maybe should test my new ground for the plasmatable. I only got a cheap multimeter, so I read how to do it easy with that.

But why do I get 0.258 Vdc when i stick new ground rod and neutral together? and -0.04 Vdc when old groundrod (2 years ond) and neutral together?

Hope you can help here.? :)
Hyper that plasma machine needs to have its on dedicated circuit with nothing wired to it
 
So now I think i maybe should test my new ground for the plasmatable. I only got a cheap multimeter, so I read how to do it easy with that.
Hi - unfortunately you can’t test the impedance of your earth rod with a multimeter. Electricians usually have the right equipment to perform the test.
 
It is a purchased CNC laser, that i have build a plasma on.
Looking at the photos I am not surprised you have problems. The control electronics should be in their own solid metal screened enclosures and well away from the power leads. Earthing should be back to a single star ground point. Signal and control commons (0 volts) should be separate wires inside screened cables and the screens only connected at one end of cables to the star point.

EMC/EMI issues are very complex and a mixture of deep EMC knowledge and plenty of practical EMC experience. You can't just lash things up like that in a plastic box and expect it to work just fine. It generally will not do so. It will have little (if anything) to do with your Ground Rod. You will also need FAR more than just a multimeter and also the experience and knowledge how to use EMC diagnostic equipment including RF sniffers and spectrum analysers if you still had problems after building it in a proper manner in metal screened boxes and suitable well routed cabling, which may be all you need to do to get it to behave.

In my opinion the best book by far is 'EMC for Product Designers' by Tim Williams. EMC for Product Designers: Amazon.co.uk: Tim Williams: 9780081010167: Books - https://www.amazon.co.uk/EMC-Product-Designers-Tim-Williams/dp/0081010168/ref=sr_1_1?keywords=EMC+for+product+designers&qid=1568580182&s=books&sr=1-1 The first Ediion was written in 1976 and the latest 5th Edition in 2016. It is 550 pages and quite expensive but is an excellent guide.
 

Reply to Ground rod and EMI issue in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Now I understand why so many people in US have stories of computers blowing up during thunder storms. This is a pretty dumb rule for ground...
Replies
2
Views
474
Hello All I was pondering an idea recently regarding the ground connection to my property. At present it has a combined Neutral to earth at the...
Replies
8
Views
1K
Hi All, I own a country Villa out in the Spain countryside. Was having problems with water pressure so local tradesmen advised to get a water...
Replies
14
Views
972
Morning all, Really hoping to get some advice / confirm what a few of us are thinking about a job in the future. Back ground - We have to swap...
Replies
15
Views
385
Hi guys, im currently trying to start my new big block chev in a chevelle but having issues.. im a full novice on electrics so be gentle ! The...
Replies
2
Views
243

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock