i was thinking of the installation i have nearly completed and i was thinking about the grouping factor issue, the cables are grouped in pvc trunking leaving the consumer unit and travel about 4 meters before entering ceiling before dispersing into seperate circuits.would a correction factor be needed?
it says in a book i have that no correction factor need to be aplied if entering cu as vairying size i won't mention the authors name
 
if in trunking, with plenty of space, then forget grouping factors.
 
If any of these circuits are carrying less than 30% of the cables rating (taking account of derating for temp, insulation ect), then they can be ignored for grouping.
it's down to your judgment really. As long as you can justify it, backed up with best practice ect.
Another relevant point is that if you have to apply derating factors, for environmental conditions, but they apply at different parts of the circuit, the. Only the. most severe derating may apply.
 
It says beneath table 4C1 "These factors are applicable to uniform groups of cable, equally loaded". - Which would suggest the theory you have found to be true.

It also says "If, due to known operating conditions, a cable is expected to carry not more than 30% of its grouped rating, it may be ignored for the purpose of obtaining the rating factor for the rest of the group" - which kinda contradicts the first point as it is suggesting different loads within the grouping..

Interpretation is a wonderful thing. I will flick through some of my books to see what examples are given of this to see if it helps.. personally, I would take the same opinion as Tel.
 
lighting and sockets.
anyways thanks for the response and for once for me a good one.......happy days! and a good nights sleep tanks

- - - Updated - - -

by the way the book was brian scaddans fifth eddition.
 
I will flick through some of my books to see what examples are given of this to see if it helps.. personally, I would take the same opinion as Tel.

I seen this on I&Ts in hotels, DBs feeding 20 odd bedrooms with bundles of T&E tie wrapped together spewing out from the DB, but within a few metres going their separate ways. Lightly loaded I should imagine.

I/We await your verdict widdler.
 
I think that if the cables run through insulation further on in the circuit ect, and have been derate for that, but there is no insulation where the cables are bunched near the DB, then You can ignore the grouping. Obviously this can't be a blanket rule, and you must use common sense and your experience. What is the cables current carrying capacity, compared with the MCB size? This can be another tool to help you come to a decision on whether it's acceptable.
 

Reply to grouping factor question in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, I am currently doing a level 2 (2365). We have been doing trunking factors and I am not sure about if you need to apply the 45% space...
Replies
3
Views
458
I am a lecturer teaching electrical installations and in reading through the on-site guide to prepare a lesson I have come across a section I have...
Replies
4
Views
2K
Im running a ring main for all my sockets using 2.5 cable....as an after thought i was thinking to spur off one of my socket outlets and run up...
Replies
4
Views
509
I have injured my back and I feel it is only going to get worse over the years. My plan is to get a lad to help out 2 days a week. I'll be...
Replies
12
Views
2K
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
776

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock