DuncanS
Hello Sparks, I'm quite new to all of this having quite recently gotten my certificates in the post. Today I started down the road of having my NAPIT inspection and I've come up with a concern whilst designing the circuits for installation... I'm installing a 10.2kw oven and a 9.5kw shower... After accounting for diversity on the oven I have settled on 6mm T&E 27 meters with a 32a breaker and 10mm T&E for the the shower with a 45a breaker for 15meters... Both clipped direct to wooden joists and plasterboard. I have accounted for an ambient temperature of 50*c as both circuits will be in the loft for a decent portion of the cable run... All checks out fine in terms of volt drop... My two questions are 1) how far apart do I need to clip the cables from each other in order to avoid any derating factor? 2) neither cable runs along side any other cables but I have no choice but to cross other circuits on three occasions, they will cross the path of a ring final circuit twice and a lighting circuit once, do I need to account for this in my calculations?
Thanks in advance to anyone who can help
Thanks in advance to anyone who can help