Thought id start a thread for posting those unusual faults that have you scratting your head for age, feel free to post one for a guessing game but here goes with mine....

Call out to a work yard who have a metal container cabin decked out with a few sockets and lights, the problem was nothing worked and they had checked mcb's and rcd's.

So just to clue you up and no i didnt wire it but this is how i found it... 180amp 3ph generator feeding a dist' board DB1 in an adjacent cabin- off this DB1 it also fed a small consumer unit in same cabin DB2, it was a front end rcd on this board and one of its outgoing circuits fed the steel container dist' board DB3 that was having problems.

First i check DB2 rcd and outgoing mcb were on --- yes
Then i opened DB3 and checked for voltage --- L-N Ov / l-E 230v / N-E 230v (note single phase board)
Next i checked the power in DB2 ... front end rcd L/N input 230v --- rcd output L/N 0v
rcd output to E was L/E 230v & N/E 230v
This rcd was in the on position what was my fault and why was i getting 230v N/E and L/E when i had switched off the mcb powering DB3 (note mcb was working fine)

Hope you took all that in lol

I just add for more confusion ... DB2 and DB3 had front end rcd's 30mA and the sockets off DB3 were RCD sockets....YEP!!! crazy :6:
 
Last edited:
If i turned off the mcb feeding the DB3 i lost the L/E 230v as expected in DB3 but retained 230v N/E Why?
 
Last edited:
it was the only circuit on DB2 but you spotted missing voltage so why have i got the 230v N-E then if i have no outgoing feed.... took a while to figure this out even checked the gen's N/E link was connected to which is was.
 
You close Plugs but il let you know now and was a bugger to work out but elimination is the beast and thus the most unlikely becomes the likely.

DB2 -DP fron end RCB or RCCB if you like had tripped and when reset had mechanically latched but not closed Neutral fully and on top of this the test button was pressed by customer trying to get power on now in doing so it created a high impedance circuit using all the outgoing devices to create a false N as its tapped of the outgoing side of the RCD and with no true N available it used the all the neutral outgoings to create enough current to weld the test button contact together...... so i had no true neutral and a 230v potential to earth from any outgoing N thus turning the DB3 mcb off didn't isolate the neutral going to DB3 and through connected loads.
 
Strewth, it reminded me of an EICR i was doing. A number of snap cabins with SP Dbs with front end RCDs. After pressing the test button, bloody thing conked out so no power and shift break in 40 mins. EEK - needless to say i legged it.
 
no neutral continuity through RCD. buggered RCD.
 
Its probably a 1 in a million due to the mechanism not latching correctly which could have stopped it tripping with the test button as well as either mechanically jamming the test in or welding it closed which i see less likely.... was a three way failure of the device but allowed feed through initially then High Impedance fault back up Neutral due to jammed test mechanism.
Nightmare to work out especially with 3 sets of 30mA rcds in a line, it just didn't make sense, i even had them shut genny down so i could verify the N/E link was functional and not loose.

Always a school day :whatchutalkingabout
 
no neutral continuity through RCD. buggered RCD.

Answered in post 10 tel and your correct but not fully you wouldn't get 230v N/E in D.B3 if the mcb feeding it was switched off liked i found, as mentioned in my OP this is for the serious head scratches i would have quickly realised just a broken N and not thought it worthy posting.
 
Last edited:
starting with your r1 and r2 wouldnt of helped me this time...

- - - Updated - - -

but could of lent them an extension lead and dispossed of 3rd board
 
I missed explaining the full test sequence to get to the relevent by this point id already disconnected the suspect feed cable and did all relevent tests on it and it really was the fact that turning the supply mcb off still left 230v N/E at DB3..... was quite a relief when my next breakdown was a drive or encoder fault ;)
 
if that had hgappened to me i would of thought polarity was wrong

- - - Updated - - -

id be turning in circles and scrathchin the scalp
 
if that had hgappened to me i would of thought polarity was wrong

- - - Updated - - -

id be turning in circles and scrathchin the scalp

All was checked 3ph genny up to DB2 and with DB3 breaker on the L1 became live 230v to earth and 0v L/N in DB3 so couldn't be polarity they were both at the same potential on same phase but i doubt il ever see this fault again but it been 20 odd yrs in the waiting
 
Told you before Geordie you may be of scottish descent so come on ower the dyke neebs. ya ken ya wanna

I have to say that when I was working in the Rock & Roll business and latterly in Exhibition Contracting I did enjoy working "over the border". It was guaranteed to be well looked after & to have a great time. One of my fondest memories was working with the crew at the Glasgow Theatre Royal & the party that followed. :17::54:

Great lads the Jocks ...... I'd rather work with them than Mackems any day. :wink_smile:
 

Reply to Guess the Fault??? in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
Replies
1
Views
568
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi all, After some options/opinions on fault finding N/E fault on ring final as fairly newish to being out alone. Customer wants to upgrade from...
Replies
7
Views
1K
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
Hello All and happy new year. Over the holiay I have changed all of my old sockets to some nice new ones and added a couple with usb sockets for...
Replies
4
Views
735

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock