Molly17

DIY
Reaction score
1
Hi...a bathroom company has fitted an electric shower 9.8kw, we have just found out our cable is 6mm. They had a plumber and a chap who was not a qualified electrician do the first fix of fitting the shower and also putting in down lights in the ceiling and they got an electrician to 2nd fix. We haven’t yet had any certificates from them for the electricians work. Should I say anything to them or is everything fine with this?? Advice would be appreciated. Thank you
 
What size MCB is the 6mm cable protected by?
How long is the cable and how is it installed, does it pass through insulation at any point in its run?
 
What size MCB is the 6mm cable protected by?
How long is the cable and how is it installed, does it pass through insulation at any point in itsCD530117-CAC4-46C0-A6F9-42D8692FE287.jpeg59757290-8826-42FC-B821-94816D17667D.jpeg run?
Oh I’ve no idea, can you see what you need from the pictures? The box is in our garage and the bathroom is upstairs, the cable as far as I know goes into attic and then into bathroom inside the plastered wall
 
The new shower will draw a current of over 40a, and it is on a 32a device. Not compliant. Whether the 6mm supply cable is adequate depends on the length and way it is installed, but I would think it is most likely that a 10mm cable would be required. However it is unlikely that in it's present form it is dangerous, or will give any trouble. The circuit is only loaded for relatively short periods....(unless my daughter is using it). A lower rated shower and replacing the 32a for a 40a device (if installation method allows) would have been the way to go.
If the shower is a straight replacement no certification is required, if wiring has been installed or altered then it is, same for the downlights.
 
Do you have two electric showers? And I see you have a 40A cooker supply.
Hi yes we have an old shower in the en-suite which is I think 8.7 kw. My oven is electric neff double oven with a gas hob
[automerge]1583218272[/automerge]
The new shower will draw a current of over 40a, and it is on a 32a device. Not compliant. Whether the 6mm supply cable is adequate depends on the length and way it is installed, but I would think it is most likely that a 10mm cable would be required. However it is unlikely that in it's present form it is dangerous, or will give any trouble. The circuit is only loaded for relatively short periods....(unless my daughter is using it). A lower rated shower and replacing the 32a for a 40a device (if installation method allows) would have been the way to go.
If the shower is a straight replacement no certification is required, if wiring has been installed or altered then it is, same for the downlights.
There was a shower there before, but an old one with less power. The down lights are new. I wasn’t sure if an electrician should have done all the work and not just come at the end to check it was ok? The only reason I am questioning this is our other shower needs replacing and when we went to look for one they asked us about the size of our cable and said we couldn’t have a high kw shower, which then got us worrying about the one we have recently had fitted and if they have done the lights ok, because they didn’t mention the cable size to us
[automerge]1583219220[/automerge]
Hi yes we have an old shower in the en-suite which is I think 8.7 kw. My oven is electric neff double oven with a gas hob
[automerge]1583218272[/automerge]

There was a shower there before, but an old one with less power. The down lights are new. I wasn’t sure if an electrician should have done all the work and not just come at the end to check it was ok? The only reason I am questioning this is our other shower needs replacing and when we went to look for one they asked us about the size of our cable and said we couldn’t have a high kw shower, which then got us worrying about the one we have recently had fitted and if they have done the lights ok, because they didn’t mention the cable size to us
DD6C782F-B683-45C1-9406-2EBB1721321D.png
 
Last edited:
Basically they've fitted a shower that's too big for the breaker and if the breaker isn't tripping it's more by luck than judgement I would say. I wouldn't have thought any thing would come to any harm from it but it's not what I would have done myself
 
Got a similar one last week, customer had fitted a new shower and complained that it tripped if he and his wife had a shower right after the other, or when the daughter was using it. 8kW shower 35A on a 6mm circuit with a 32A RCBO. Majority of the circuit is clipped in the cellar so I am going to fit a 40A RCBO. Not ideal but compliant.
 
Got a similar one last week, customer had fitted a new shower and complained that it tripped if he and his wife had a shower right after the other, or when the daughter was using it. 8kW shower 35A on a 6mm circuit with a 32A RCBO. Majority of the circuit is clipped in the cellar so I am going to fit a 40A RCBO. Not ideal but compliant.
I wouldn't expect 35A to trip a 32A MCB or RCBO, are you sure that's all the load is and it's not something higher?
 
Lol had exactly the same last week, 8.5KW shower tripping 32A MCB, had been 'ok' for several years. Clamp meter read 35A. I can't see a 32A MCB holding for too long at 9.5KW.
 
Lol had exactly the same last week, 8.5KW shower tripping 32A MCB, had been 'ok' for several years. Clamp meter read 35A. I can't see a 32A MCB holding for too long at 9.5KW.
Probably will hold for the duration of a shower, or even longer. But it'll stress the mcb over time and eventually it'll start tripping rather more promptly.
 
Probably will hold for the duration of a shower, or even longer. But it'll stress the mcb over time and eventually it'll start tripping rather more promptly.
Yes this must be the case, the 'available showering time' was getting shorter and shorter. Unless the transformer taps were recently changed and the supply voltage went up!
 
Lol had exactly the same last week, 8.5KW shower tripping 32A MCB, had been 'ok' for several years. Clamp meter read 35A. I can't see a 32A MCB holding for too long at 9.5KW.
I came across one a few months back while installing a cooker. It had been installed by the home owner, he claimed it was 10.8kW, and swore they'd never had any problems with the MCB tripping. 32A breaker/6mm² cable.

Pulling a current of 1.46 times the rated current of the breaker, it could take up to 1 hour to trip (or so I am led to believe)
 

Reply to Has the correct shower been fitted? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, my niece lives in a flat and has a bathroom without a window. There is an extractor fan which packed up and an electrician installed a new one...
Replies
4
Views
711
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hello, hello, long time listner, first time caller... So, I have an issue in a house I'm trying to get ready to rent. The plumber has installed a...
Replies
17
Views
2K
Hoping someone maybe able to help. We have a Horstmann electronic 7 that's connected to the water heater element(everything been great for years)...
Replies
3
Views
1K
Hello, Is there an actual age limit on house wiring that would prevent a traditional fuse box being replaced with a consumer unit please...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock