vbyrne

-
Reaction score
6
I have been trying all last week to try to get two pumps to work together as well as work indepently of each othe Ill explain. I have a three channel time clock HW,CH1 and CH2 I have a oil fired burner and two pumps.When I call for CH1 or CH2 I want the two pumps to run when I call for hot water only I want one of the pumps to run and I have a fire with a back boiler that heats the water and that will bring in the other pump to run some one has told me that I have to use a relay I know very little about using relays could some one please help me out:confused:
 
just been trying to think but it is late and there would be a way of doing it with the s/l from the valves without the need for a relay i think but i dont understand why you would need to? Could teh plumber not incorporate a seperate pump that could be fired up for the hot water?
 
just out of my time and the only thing i dont understand is heating,basic heating in general,has any1 a good way of explaining it simply?sorry to get off subject.
 
Heating piece of cake, 2 systems generally used, a Y plan which is one valve that controls the hot water and heating or, S plan which is 2 or more valves which controls different zones, the S plan is IMO a better way of controling things and easier to expand on.
 
Only do you need both pumps to run when the CH is turned on? As stated by sparks the plumber needs to plumb the heating to either a S, Y plan. I have tried to wire something like this before it just turned out to be a big headache and the plumber was called back to put in the job right
 
2 pumps require you to install a relay otherwise there is a common path via the boiler to both pumps, which means that any time that one pump is called upon to operate a signal will go from the boiler to the other pump.

Hope this helps.
 
I think the situation would be made far easier by having a motorised valve installed onto the hot water feed.

A 3 pole relay is required to accept the 3 incoming call signals with a common output signal to each pump.


Having pondered on it some more it would appear that as you will have 2 input signals to one of the pumps, a further 2 pole realy may be required
 
Last edited by a moderator:
Sorry about the size, I didnt realise it would be this big! I also assumed the voltage was 240VAC and that they would be single phase motors?

Heatingcontrol.jpg
 
Last edited by a moderator:
you need chan 1 and 2 to be seperated via relays or else the 2 zones will come on together

Think we need some better idea of what is actually required, is the back boiler the only boiler in the system?

This would be so simple if there were zone valves (2 port) installed
 
Last edited:
Do you want both pumps to run when ch1 or ch2 is calling or pump 1 when ch1 is calling and pump2 when ch2 is calling?
 
PHP:
Thanks lads for all of that,Lenny is right there will be two signals going to the heating pump one from either of the heating CH,which will come on with the other pump as well and another signel that will bring on the pump on its ownwhen hot water is called for on its own the only time the other pump will be on is when the stat on the back burner calls for it to pump water away from the cycindier so kep on going lads we are making good progress:eek:
 
I've made a drawing in word of what I think you need but I don't know how to up load it to the forum.

Can anyone advise me on this.

Basically you need a 3 pole relay, ch1 feeds the common of the 1st pole, n/o & n/c both go to pump 1.
ch2 feeds the common of the 2nd pole & the n/c feeds pump 2 & the boiler, n/o is not used. These 2 commons are linked.
A permenant live feeds the common of the 3rd pole and the n/o feeds the boiler & pump2, n/c is not used.
The coil is fed from the hot water demand.
This way if hot water only is called for pump2 & the boiler will be on but not pump1.

I hope this is clear but I can post a basic drawing if someone tells me how.
 
Right lets get to the bottom of the requirements.

Channel 1 requires pump 1 and pump 2 and the back boiler to come on
Channel 2 requires pump 1 and pump 2 to and the back boiler to come on
Hot water requires pump 1 and the back boiler to come on

Is this correct and is there anything else involved
 
andyb I think you have it nearly cracked but you are talking to someone who has never rally worked with relays before,from what you are saying I can get a relay from the wholesalers with three different sets of terminals each one will have its own set of common terminals so in fact a relay is just a two way switch that is switched with the coil am I right in saying that
I've made a drawing in word of what I think you need but I don't know how to up load it to the forum.

Can anyone advise me on this.

Basically you need a 3 pole relay, ch1 feeds the common of the 1st pole, n/o & n/c both go to pump 1.
ch2 feeds the common of the 2nd pole & the n/c feeds pump 2 & the boiler, n/o is not used. These 2 commons are linked.
A permenant live feeds the common of the 3rd pole and the n/o feeds the boiler & pump2, n/c is not used.
The coil is fed from the hot water demand.
This way if hot water only is called for pump2 & the boiler will be on but not pump1.

I hope this is clear but I can post a basic drawing if someone tells me how.
 

Reply to heating control pumps in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

I've always thought I was quite good a wiring heating systems, I can do Y plan, S plan, UFH set ups, "normal" thermal stores etc, you name it and...
Replies
4
Views
890
For the past few years, I have used a hydronic system (outdoor wood boiler) with both high and low temp working simultaneously. The low temp...
Replies
6
Views
753
I've pretty much sussed out the wiring for the radiators and underfloor heating, thanks to help from the forum. I do have one more question...
Replies
6
Views
641
Hi all, taken on a new build project and they have quite a large property with three separate manifolds. I have wired before with one manifold but...
Replies
11
Views
1K
I have a 4-wire well pump (red, yellow, black, and green) which just quit. Cycling normally, then shut off and never came back on. I've gathered...
Replies
3
Views
660

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock