Hello guys and girls been using the info on this great site now for about 6 months never needed to join and ask questions because of the handy search button ^^^
I understand that unless omitted (RCDS, disconnection times achieved, main sup bonding on water, gas, Ect.) bonding must be done across all exposed/extraneous conductive parts inside a room containing a bath or shower.
i also understand that the resistance must be low so that volt drop must not exceed 50v when carrying the operated current of the protected device (r < 50 / Ia) for a 30ma RCD (50 / 0.03 =1667) and if metalwork to MET (person likely to be wet) 50k ohms or higher and 25k ohms (person likely to be dry) does not need bonding.
My question is:
At a existing installation without RCD protection if you where to mesure the resistance between the hot and cold pipes under a bath and found a reading of 0.01 ohms would you assume the pipes have been earth bonded (maybe the bonding is not visible) what min ohm's reading acceptable and how do you work it out???
Another example is you replace a shower like for like on a circuit with RCD protection and find a high ohm's reading between the showers earth terminal and the pipework (maybe a qualified plumber has used a pvc push fit between the metal pipework:lol what would be the min acceptable reading you would expect and how do you work it out.
I really hope these questions make sense. i've got all the books OSG, BS7671, john Whitfields electricians guide, guide to Part P and i must be missing something or being stupid knowing me probably both
Thanks in advance.
Martin
I understand that unless omitted (RCDS, disconnection times achieved, main sup bonding on water, gas, Ect.) bonding must be done across all exposed/extraneous conductive parts inside a room containing a bath or shower.
i also understand that the resistance must be low so that volt drop must not exceed 50v when carrying the operated current of the protected device (r < 50 / Ia) for a 30ma RCD (50 / 0.03 =1667) and if metalwork to MET (person likely to be wet) 50k ohms or higher and 25k ohms (person likely to be dry) does not need bonding.
My question is:
At a existing installation without RCD protection if you where to mesure the resistance between the hot and cold pipes under a bath and found a reading of 0.01 ohms would you assume the pipes have been earth bonded (maybe the bonding is not visible) what min ohm's reading acceptable and how do you work it out???
Another example is you replace a shower like for like on a circuit with RCD protection and find a high ohm's reading between the showers earth terminal and the pipework (maybe a qualified plumber has used a pvc push fit between the metal pipework:lol what would be the min acceptable reading you would expect and how do you work it out.
I really hope these questions make sense. i've got all the books OSG, BS7671, john Whitfields electricians guide, guide to Part P and i must be missing something or being stupid knowing me probably both
Thanks in advance.
Martin