Hi,

This is my first post, although I have been browsing the forums for a little while now.

I work in BMS and have my AM2 on friday. The nature of my work means I don't get to test so there are a few things I'm unsure of and was hoping for some clarification.
I know for some people they may be obvious but I don't want to make any small mistakes and I want to be as prepared as I can be.

I know its a lot of questions but I'd be grateful with whatever people can clear up, specifically on the I.R tests.


General
1. Does the banjo bolt at the cu go inside and face out of the cu
2. does the SY between the DOL and motor only need to be banjo'd at one end as its for interference and not earthing?


Testing Sheet
1. would the AM2 bay be best classed as industrial or commercial so I know how long to put the next inspection due in part.

2. When I measure Ze I know to put the figure down as Zs at DB but on the installation certificate can i put this down too, as its so close to the main incoming supply it would be acceptable.

Testing
1. Should I write my water and gas R2 readings on the test sheet or just on the back of the sheet?

2. I was told we should take all notes on the back of the test sheet but I'm concerned about losing time doing this.
I know I will be doing the R1+Rn & R1+R2 table for the ring final to write down all figures, and I will write down my RCD trip times, Ze, PFC etc.
But do I need to calculate my expected R1+R2 figures using the Resistivity of the cable size x cable length and divided by 1000 to comapre them to measured figures?
I know this will tell me what I should be getting but as I said I'm concerned with losing too much time.
Also, if my R1+R2 figure at each socket are more than 0.05 ohms +/- would I be expected to fix this or is it fine to leave if it isn't overly high? (I know the spur will be higher)

3. I'm pretty sure Im ok with this but I just wanted confirmation. After I do my r1, r2 & rn readings for the ring final, if I add togetehr say, r1 and r2 and divide by 4 then that will be my expected R1+R2 reading right?

4. for the heating system I know I need to do the R1+R2 test up to the FCU to record on the test sheet, but I need to check continuity at all relevant points after the FCU.
And what would be the best way to do that; wago the cpc and line together in the wiring box/JB and test at each point like normal?


I.R tests
I'm worried about not disconnecting all things that are vulnerable to damage when testing. I plan to do the following:
* disconnect light
* Replace ring final RCBO with 32A MCB. If 32A MCB is not available is any size ok as its only a low current passing through so for testing purposes it could be even a 6A right? Or would they not accept this.
* Remove carbon monoxide detector
* ensure Isolator for TP+N socket is on

What I'm unure about is:
* When a FCU/SFCU has a neon, can I just disconect the flyleads and should I just put them in a wago?
* If the heating circuit is not on a switched spur can I just remove the fuse before testing?
* I know I need to do the Cu to the DOL and then the DOL to the motor but will leaving the conductrs connected damage the DOL. Should I disconect and wago, and If i do can i not just connect the incoming cables to the outgoing cables of the DOL and not have to do a second I.R test?
* When doing the lighting, I'm getting confused how many times to operate the switches to cover all combinations. There's a feed to the first two way, then intermediate and then a 2 way and then upto the light, can anybody shed some light into the process of this.


Any input is appreciated.


Thanks,

George
 
Mods, please move to the trainee forum, no replies out here.
 

Reply to Hello & Help with AM2 in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi Guys, sorry if posting in the wrong section. I am due to start 2391-52 course soon, and there seems to be from what I have found out, a 3 phase...
Replies
6
Views
391
I recently just done my AM2 resit and in my inspection and testing, despite the invigilator watching me do the tests, I think I may have forgotten...
Replies
0
Views
928
Hello everyone, I saw in the hospital every circuit has 2 separate cpc, same size, sometimes different. I'm wondering. How we can do the dead...
Replies
1
Views
865
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Today I was doing an EICR and went around a couple sockets with a Megger MST220 socket tester just to see if there was anything obvious, all three...
Replies
20
Views
638

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock