Hi all, having major problems with the mains on a TT system. Customer requested new position for CU and to get supply moved by electricity supplier. Now customer won't pay for it after getting a quote from them. The new CU position is approx 6 mtrs away from meter and i'm wondering what the best/safest way to do it is? Did my 17th regs recently but can't find an answer in the big red book. The 1st 2 mtrs the cables can be sitting on joists but the next 4 are in joists and i'm a bit duboius about running d/ins tails through them. Might be o.k but i need to be 100%.
Thanks in advance,
Dan
 
Hi Dan

You'll need to make this a sub main as it is 6mtrs. You'll need an RCD and isolator on the tails ( 100amp 100mA type s ) if you are using double insulated tails.
Or you can use SWA and use a fused isolator.
On top of joists is not good but have seen plenty running through joists as long as the correct depths and diameters of hole are achievable.

Mark

----------------------------------------------------------------------------------------
This is my understanding but I'm happy to be educated.
 
Thanks marcus, that's helped. The" on top of joists bit" refers to a void where no boards are going to be laid on top, thought that would be better for heat dissipation rather than going through them?
Thanks again.
 

Reply to Help!!!! My tt system mains question! in the Australia area at ElectriciansForums.net

Similar Threads

Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
880
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi guys I was recently ask by a customer if/how his house could be supplied by his electric car. He wants to charge the car at night on low rate...
Replies
4
Views
1K
Another question! I'm designing for a TT system, there's going to be one 10 way Rcbo consumer unit for the house, less than 3 metres away from...
Replies
3
Views
2K
The installation is TT. The meter box has been moved by the DNO. The tails will now be >3m so I will be fitting a switch fuse. I was planning on...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock