arturas

Hi there guys, just to be sure I wanted to double check with someone more experienced. Usually all my work is re-wiring of properties. Now I need to feed up the top flat. The run will be roughly 45-50 meters, with a 60a fuse.
Now when calculating the voltage drop, as there will be lighting circuits it has to be 3%. I'm thinking of 25mm three core swa. It will be run on the tray next to other cables feeding other flats. And when calculating the voltage drop I'm using column z of a table 4d4b which is 1.75 per amper per meter: 1.75x60x50/1000= 5.25 which is < then 3% of 230v. And now when trying to determine a cable size I'm using a formula: In/CgCaCsCdCiCfCc . Because it's above the ground in free space no thermal insulation and the ref method is e, all of the factors =1 except the grouping factors which is 0.72. In that case I get 60/0.73= 83 which is less then maximum current carrying capacity of 25mm cable. Am I right?thanks for any help!
 
You are planning for the worst case scenario there with a design current of 60A but this will mean that you are very OK with that supply cable and this would allow for some leeway should the fuse be uprated to 80A. If the customer will accept it then go for it; remember to earth the armour!

So long as your description is accurate then the cable is fine.
 
Thanks for a quick reply! It is the worst case scenario, but the fuse is 60 amp and it will hold a bit more before blowing so the cable has to as well.
 
As Richard has said. You cant go any smaller in the cable size as 16mm has a VD of 8.4V which is 3.6%
If they upgrade the fuse to 80A, as mentioned above by Richard, then the VD gets really close... 7V or 3.043% but you can only do the calcs to what is there now and not what may possibly happen in the future.
 
Just out of interest.. where is the cable tray being routed to go to the top floor?
 
Cable tray is visible hanging of the ceilings, it's a big landlords aeria with a factory look, so everything is visible,metals,trays, plumbers pipes and etc
 
As Richard has said. You cant go any smaller in the cable size as 16mm has a VD of 8.4V which is 3.6%
If they upgrade the fuse to 80A, as mentioned above by Richard, then the VD gets really close... 7V or 3.043% but you can only do the calcs to what is there now and not what may possibly happen in the future.

I understand that, I can't see a need to upgrade a main fuses, 60amp for 2 bed flat is plenty enough, however I will install a 60amp fused isolator so even if they would, the cable would still be protected.
 
This is the way your DONT want to do it, cram all those 16mm cables off 80A landlords fuses into a bit of trunking and start running them up 4 storeys to 8 conveted flats throughout the building with everything run of electric (kitchen, heating & water) ..... and while you're at it put in a CU for the communal areas/fire alarms/emerg lites and dispense with the protection around it!

Picture quality not that good as the camera phone was shaking a bit at the time - I was just starting to get my first overall initial impressions before completing an EICR post the local council refusing to re-register the property.

Not my install I hasten to add but done by a reputable "electrical contractor" who pride themselves on 'time served' electricians!! (In fairness I think the consumer unit had been damaged after the install)
 

Attachments

  • 01_Insp.jpg
    73.1 KB · Views: 78
  • 01_Insp.jpg
    96.5 KB · Views: 80
I wasn't even thinking of running 16mm I wanted to be sure that 25mm is big enough. Wow that install is on another level! I would like to book an yearly assesment on that one for a joke, I think 500£ would be worth seeing guys face! :)
 
This is the way your DONT want to do it, cram all those 16mm cables off 80A landlords fuses into a bit of trunking and start running them up 4 storeys to 8 conveted flats throughout the building with everything run of electric (kitchen, heating & water) ..... and while you're at it put in a CU for the communal areas/fire alarms/emerg lites and dispense with the protection around it!

Picture quality not that good as the camera phone was shaking a bit at the time - I was just starting to get my first overall initial impressions before completing an EICR post the local council refusing to re-register the property.

Not my install I hasten to add but done by a reputable "electrical contractor" who pride themselves on 'time served' electricians!! (In fairness I think the consumer unit had been damaged after the install)
Saw work like this on a farm, it was done by a Polish 'electrician'.
 

Reply to Help needed for choosing a cable to feed a top floor flat. in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
404
Hi All, I have a client who is developing a plot of land for a single house. Currently, their 100 amp service cut-out is in a cubicle fed by...
Replies
7
Views
1K
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted...
Replies
20
Views
2K
I am in a bit of a pinch at the moment and trying to argue a massive amount of used of electricity with my provider which I find it hard to...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock