R

rod1924

New dual RCD CU fitted today. IR tests ok for circuits up and down albeit UP has only L/N into CU. Put on separate RCD's, down ok but up trips both RCD,s. Tried both in one MCB: Down ok till turning on any up light then RCD trip

Any help really appreciated as brain frazzled
 
Shared neutral most likely suspect.
 
Hi rod, burrowed neutral sounds likely but when u say u tried them both in same mcb and they tripped, had u put the neutrals onto the same bar also?
Id take a look at the landing/hall 2-way as this is normally the culprit, pinch a neutral from the nearest light
 
New dual RCD CU fitted today. IR tests ok for circuits up and down albeit UP has only L/N into CU. Put on separate RCD's, down ok but up trips both RCD,s. Tried both in one MCB: Down ok till turning on any up light then RCD trip

Any help really appreciated as brain frazzled
whenever undertaking a C/U change on an install....can you please IR test between the neutrals first to make sure their clear..Thank you.
Glenn.
 
Thanks for the replies (I knew it was a borrowed neutral) but I am looking on a fix to solve the issue (N were terminated together...answering previous questions).

Last job was the same (borrowed N) but with RCBO's. Using one RCBO solved the issue....and borrowed N stated on Installation Report.

So, any other remedies?
 
Thanks for the replies (I knew it was a borrowed neutral) but I am looking on a fix to solve the issue (N were terminated together...answering previous questions).

Last job was the same (borrowed N) but with RCBO's. Using one RCBO solved the issue....and borrowed N stated on Installation Report.

So, any other remedies?
What!! You left a potentially dangerous condition in an installation and noted the fact on an EIC? You should have remedied this or at the very least informed the customer and issued a danger notification cert signed by both parties if they refused to get this seen to! at least you would have coveted yourself! Or was this an EICR you was carrying out?
 
FFS Rattlehead, obviously the client was informed but would not pay for remedial work. Advice sought from my body and all details recorded. But thanks for the advice
 
Thanks for the replies (I knew it was a borrowed neutral) but I am looking on a fix to solve the issue (N were terminated together...answering previous questions).

Last job was the same (borrowed N) but with RCBO's. Using one RCBO solved the issue....and borrowed N stated on Installation Report.

So, any other remedies?

Please tell me this is in your own home?? If its a paying customer id be a tad upset.

As for sorting it. What load is on the two lighting circuits? Either create one circuit if its not going to become overloaded.. or sort your borrowed nutural problem.. Its basically one circuit sharing a nurural from another circuit. Usually the landing light to save running 3 core upstairs..

If you have to ask how that is corrected then i have to question your ability..

You a qualified spark mate?
 
Seems to be a slight contradiction from the OP moving through the posts.. From not having a clue in post one and knowing the fault once told.. Dont try and pull the wool over peoples eyes..

Its so blooming obvious..
 

Reply to Help needed on lighting circuit please in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
601
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I need your help please once again in tracing a fault. Am DIY but not clueless. Converting former kitchen into 2 rooms: bathroom and laundry. The...
Replies
24
Views
2K
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
567
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock