714gold714

Hello there basically i rewired a 3 bedroom house about 9 months ago tested out fine and have had no problems at all.

However received a phone call today from customer saying that all power has gone off, arrived and found that on the dual RCD board i fitted i would switch on the shower circuit (switch on at button on shower) which is powered by the 2nd RCD and switch on the 1st RCD powering kitchen lights it will trip the 1st RCD. In the end i totally disconnected the kitchen lights and the shower worked perfect and all the other circuits but as soon as the kitchen lights are connected it trips.

The circuit is not being over loaded as i have done a clamp test etc

Also when I had the kitchen lights on if i plugged anything into the sockets it would trip, it just seem as soon as a load is applied with the kitchen lights on it trips.

I have had done insulation resistance but my tester was playing up im going to do insulations tests tomorow with my new tester.

Also customer said that they changed one of the bulbs in kitchen ( 12 downlights ) as when it first started the rcd had tripped

Please help lol just cant get my head around it
 
Maybe the heat from the lights have damaged the cables and this is the issue. As for the shower I don't quite understand what you've written!
 
thanks for replys i have a bad feeling its the kitchen lights there is x12 240v GU10 downlights soon as these are connected in circuit it plays up with everything. will IR soon as i find a replacement. Sorry about desciption very hard to describe
 
Hello there basically i rewired a 3 bedroom house about 9 months ago tested out fine and have had no problems at all.

However received a phone call today from customer saying that all power has gone off, arrived and found that on the dual RCD board i fitted i would switch on the shower circuit (switch on at button on shower) which is powered by the 2nd RCD and switch on the 1st RCD powering kitchen lights it will trip the 1st RCD. In the end i totally disconnected the kitchen lights and the shower worked perfect and all the other circuits but as soon as the kitchen lights are connected it trips.

The circuit is not being over loaded as i have done a clamp test etc

Also when I had the kitchen lights on if i plugged anything into the sockets it would trip, it just seem as soon as a load is applied with the kitchen lights on it trips.

I have had done insulation resistance but my tester was playing up im going to do insulations tests tomorow with my new tester.

Also customer said that they changed one of the bulbs in kitchen ( 12 downlights ) as when it first started the rcd had tripped

Please help lol just cant get my head around it
well for a start whats overload got to do with an RCD?...
 
i suspect damaged cables on kitchen light circuit causing a N/E fault. dis. the kitchen light circuit from CU ( all 3 conductors) try a continuity test N-E. if reading is > 10k ohms, then IR test N-E.
 
just trying to borrow a IR tester.

It is a complete head scratcher, he also said aswell when he canged a bulb in the downlight it didnt come on at first and he wiggled the cable and it came on so I wonder if hes pulled a connection out in junction box in the floor
 
just trying to borrow a IR tester.

It is a complete head scratcher, he also said aswell when he canged a bulb in the downlight it didnt come on at first and he wiggled the cable and it came on so I wonder if hes pulled a connection out in junction box in the floor
so is said joint box accessable?....
wants to be really doesn`t it....
 
well, that's the first place to look then. see my last offering.post 13.
 
it just confuse me why when the shower and kitchen lights are on together ( powerd by seperate RCDS) they trip when i disconnect shower kitchen lights come on, and when i disconnect kitchen lights the shower etc works fine
 
has the customer been diy-ing? its a line-earth fault for sure, maybe trapped/penetrated cable. Is there a bathroom above the kitchen tat may have leaked/ hot water pipes in ceiling ?
 
reason i suggested what i did is that i've come across a similar fault. N/E short on RFC fed from RCD2. RCD2 will not trip, even with the test button, but RCD1 trips. there are no crossed neutrals and no loose connections.
 

Reply to help needed please on fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi I have a job where customer has two families one families lives upstairs and one family will live downstairs. As the property is going through...
Replies
12
Views
627
Hi, I'm installing a Hoover oven and would like a little help please. The oven code is HOC3158IN. The oven manual states "The power cable must...
Replies
9
Views
632
An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
1K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Called out to fault on RCD tripping maybe twice in a month for sometime. Did all the tests & found RCD was faulty, Refitted a new Rcd Type A which...
Replies
2
Views
778

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock