M

Morgan keith

I'm installing an aluminium framed groundmount PV system with an SMA 17000TL inverter and wondering about the array frame earthing. The posts are rammed about 1m into the ground. Do I need to install an earth spike for each array. The Array is around 120m from the main dist panel and incomer point so have a 50mm 4 core SWA cable for the AC side. Do I need to install a seperate Earth spike for external DB installed at array or is SWA earthing sufficient?

Many thanks
 
Thanks, I was wondering if there'd be much benefit to installing an earth spike when there's already numerous big metal posts rammed much the same depth into the ground. You think I should just do an earth loop impedance test between the array frame and the new external DB supply?
 
Thanks, I was wondering if there'd be much benefit to installing an earth spike when there's already numerous big metal posts rammed much the same depth into the ground. You think I should just do an earth loop impedance test between the array frame and the new external DB supply?

My thoughts are the idea of bonding the array was to bring the array to same potential where it can be touched, not for so much fault protection, so i think if you have continuity throughout onto metal posts in the ground and the array, then the array will be at same potential where you are standing to touching the array, therefore no shock.

A earth fault loop impedance test will give you the fault loop impedance of the AC circuit, should a fault to the DC array frame occur from a nearby AC circuit. If no AC circuits are in the equipotential zone of the array ( which if the inverter is in different location to the array) then I cannot see the benefit of putting in an earth spike. Other may disagree.

But then again if you are banging supports into the ground for the array, is it much more effort to put a couple of spikes to cover your rear end?
 

Reply to help on Earthing groundmount PV array with rammed metal posts in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi everyone, I have a quick question if I may? I'm thinking of adding a second PV system to my existing rooftop PV & battery setup. As the...
Replies
0
Views
1K
I have 5 x 6m metal posts sticking out of the ground used for 200w floodlights to light up a manege. This is a domestic stables. The posts test...
Replies
9
Views
2K
This is my first posting here - I am not an electrician so please bear with me. I am trying to establish the best method to provide earthing of a...
Replies
12
Views
3K
I am undertaking EICR at a sprawling domestic over a house and several barns/guest suites, which is knee deep in C2 and C1 observations. I have...
Replies
9
Views
2K
Hello everyone, I know this has come upquite often, I have gone back through the many threads relating tothis topic. The reason for wanting to...
Replies
26
Views
15K
GEOFF S
G

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock