Discuss Help on fire proofing.. in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
E
electro
Hi
Just wanted to know a bit more on fire proofing when you are installing. what are you fire proofing and under what circumstances are you installing protection, ie fans, cables to outside. Looking on the Internet not finding much and there's not much in the BRB.
Any application, flats, houses and commercials.
Regards
Hi.
The kind of stuff we do is obviously the fire hoods for recessed light fittings between floors. Also any holes we make between floors and from inside to out are sealed with intumescent filler/fire rated expanding foam.
Agreed.
However, you may need to order sufficient quantities of expanding foam as the stairwell opening takes a considerable amount.
:D
electro i see what you mean about limited infoin th brb. In guidance note 1 selection and erection it says that the specifications for fire stopping should be detailed by the project architect or desighner for all services. and should conform to the building regs.
In the handbook thers a bit more info but to much for me to type see page 186 may help point you in the direction you need.
Nice one Lenny, Scot yea the BRB says put back what you take out in a nut shell. some of the other stuff i would like to know when should you fire proof socket outlets in what situations, what size trunking need fire stopping, risers in buildings, three storey building etc. I see they do intumescent conduit now why?.
Thanks for your help so far
I know sorry, couldnt resist:D
As for running cables in risers, i think you will find this no longer allowed in the 17th purely for this reason.
Not got regs with me at the mo, so i cant check, but then having said that, im not overly sure where you would find this.
I just seem to remember between naps on the update course, there was mention of this.
This is the canadian take on things,not BS but objectives are [FONT=&quot]the same
[/FONT]
[FONT=&quot]All penetrations of a fire separation must be sealed by an approved sealant that has a fire-resistance rating of not less then the fire partition.[/FONT]
·[FONT=&quot]Electrical wires and cables that are totally enclosed in a non-combustible raceway may penetrate the fire separation. AC90 metallic armored cable is a good selection in this case. [/FONT]
·[FONT=&quot]Electrical wires and cables, or group of wires or cables, of at least FT4 rating may penetrate the fire separation providing the diameter of the wire, cable or groups of wire or cable is not more then 25 mm in diameter. [/FONT]
·[FONT=&quot]Single-conductor metal sheathed cables with combustible jacketing of larger then 25 mm may penetrate the fire separation providing the cables are not grouped.[/FONT]
·[FONT=&quot]Combustible outlet boxes are permitted in a fire separation as long the opening in the fire separation is less then is no larger then 0.016 m2. Back to back outlet boxes, on either side of a fire separation are not permitted and must be offset to ensure the integrity of the fire separation.[/FONT]
[FONT=&quot]Part 9 Buildings: (see complete text of the NBC for all rules).[/FONT]
·[FONT=&quot]All penetrations of a fire separation must be sealed by an approved sealant that has a fire-resistance rating of not less then the fire partition.[/FONT]
·[FONT=&quot]Electrical wires and cables that are totally enclosed in a non-combustible raceway may penetrate the fire separation. [/FONT]
·[FONT=&quot]Electrical wires and cables, or group of wires or cables, with combustible jacketing, having a rating of at least FT1, may penetrate the fire separation providing the diameter of the wire, cable or groups of wire or cable is not more then 25 mm in diameter. [/FONT]
·[FONT=&quot]Combustible outlet boxes are permitted in a fire separation as long the opening in the fire separation is less then 160 cm2 in size.[/FONT]
Reply to Help on fire proofing.. in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net
On this commercial building we are refurbishing it has the above fire alarm panel which I think is pretty much brand new, I'm not even sure it was...
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Hi all, adult learner retraining and sorry if this is in the wrong place but I need help. my provider are being very cards against their chest...
Can someone please guide me on this? I have virtually no experience of home alarm systems. The client has an alarm which had been fitted to her...
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
