I have just changed a consumer unit and when i put any appliance on in the kitchen it trips the rcd i have done all the tests on the circuit and can't find a fault,any suggestions as it is driving me insane !!!!!!!
 
Instyle LED Lighting Specialists UK
This official sponsor may provide discounts for members
S

Spudnik

  • Thread Starter Thread Starter
  • #2
Either you have crossed the neutrals between the RCD's in the CU, you have a neutral in the wrong place in the CU or a faulty appliance.
 
G

Guest123

  • Thread Starter Thread Starter
  • #3
Hi.

Either a dodgy appliance, or crossed neutrals in the neutral bars in the D.B

We could be bloody twins!!!!!!!!!!!!!!^^^^^^^^^^^^^^
 
Last edited by a moderator:
G

gunny

  • Thread Starter Thread Starter
  • #4
Thanks for your help,will try tomorrow.
 

hasel5

-
Arms
You could also have a neutral to earth fault on any of the other circuits which use the rcd for protection
 