Njay

My son and his wife moved into a house about 7 months ago, they have had a new consumer unit and a new combi boiler fitted about 5 months ago and everything has been fine up until now. My daughter in-law phoned the other morning to say that the electric had gone off in the house and everytime she attempted to reset the rcd it would just trip straight off again…I told her to switch off all the mcb’s and then reset the rcd from there she turned every mcb back on one by one until the rcd tripped again and it was on the ring main that it tripped so I told her that there was something usually kettle or washing machine that is causing the rcd to trip…the last thing she unplugged was the combi boiler and then the tripping stopped and also the electric stopped on once the combi boiler was plugged back in. Later that morning I went round to pick our grand daughter up whilst I was there I just tried a few things but as soon as I turned the kettle on the rcd tripped…I said I’m pretty sure it’sthe kettle. Later that day she bought a new kettle, when I spoke with my son the next day he said it tripped again when she was hoovering and also when they used the new kettle one time???

The combi boiler sits in a utility room with the washing machine which are both plugged into a double socket. The following day I went round with my insulation resistance tester to check earth leakage on the boiler and kettle even though the kettle is brand new, but all was ok apart from the washing machine which was just over3MΩ. What I did next was to plug a rcd adapter into the plug socket then plug the boiler into the rcd adapter turned the power on and everything was ok then I turned on the kettle and then the hoover after about 30 seconds the rcd tripped on the mainboard as well as the rcd adaptor that the boiler was plugged through???It looks like a fault on the boiler…but I don’t understand… if there is a fault on the boiler why it isn’t tripping constantly and only tripping the rcd when other appliances are being used? I would be so grateful if anyone could help meunderstand what might be happening here, but be gentle it is my first post!!!
Also are thereany regs that state whether the boiler should go through a switched fused spur instead of being plugged directly into a double socket?
Thanks in advance for any help and advice given.
 
As the the CU and combi have only been installed for 5 months, get the companies back that installed them... It could well be a faulty RCD or multiples of natural/normal leakage from appliances on that circuit, or across the other circuits that the RCD is also protecting, or the internal electrical components of the combi boiler!!

BTW, what's wrong with a IR of just over 3 Meg for the washing machine, ...that's over 3,000,000 ohms??

Anyway, that would be my first step ....
 
Sounds like a loose connection in the consumer unit...possibly a N or even a crushed wires against each other which may mean an unrelated circuit can trip the RCD .. these can be tricky faults to find but if load dependent and really needs a competent experienced Electrician with knowledge of this fault otherwise you pay for scratching of heads do light loads not trip and heavy trip?..

Why are you IR testing appliances you are likely to damage them... washing machines have smoothing capacitors and electronic control boards not something you should be IR testing even at 230v as the results will be misleading.. also drop all points forward on the ring and look for a loose connection as arcing can trip RCD's

You state your a domestic appliance Engineer ... ? Not sure if this title exists in real terms as an engineer has to complete a course like HNO Or HNC to gain that title, don't tag yourself with a sales pitch title on the forum as we see through that stuff, if you had Engineer qualifications this question would not of been asked IMHO and Ive never heard it tagged to domestic appliances before with diploma or similar recognition?

Lastly welcome to the forum:smilewinkgrin:
 
Last edited:
First off all thanks for all your replies and suggestions, I'm sorry if I hit on a sensitive nerve darkwood by stating I am a domestic appliance engineer, it was just a question that cropped up when joining the forum about my job title... and that is what the company I work for call the position I hold....will see if I can rectify that in account settings maybe domestic appliance repair man will sit more comfortably with you ?https://www.electriciansforums.co.uk/images/smilies/smilewinkgrin.gif But I can assure you 100% I'm not after work or trying to sell anything just curious what could cause this problem? But back to the problem yes your right it does only seem to trip on heavy loads especially when the kettle is used...but not every time? The reason I carried out the insulation resistance test on the appliances was because I wanted to try to eliminate them out of the equation if possible and as part of my job I have access to a Portable appliance tester.I think its looking as though my son is going to have to get either the boiler people out or the electricians who fitted the consumer unit...not sure in what order though ??? In the past when similar problems have occurred in my house or friends or family its usually strait forward like a kettle gone to earth or washing machine...but I've never came across anything like this and I'm just intrigued by what could cause this type of problem??? somewhere else in the forum I read a piece about accumulative earth leakage from several appliances? could that even be it ??? Once again thanks for your help and suggestions.
 
I think the odds are in favour of the boiler being the problem - you say it doesn't always trip with the boiler plugged in, but was the boiler actually operating? If the boiler had switched itself off internally because there was no call for heat/hot water, then there wouldn't be any reason for it to trip; boiler cuts in shortly afterwards - ping, off you go.

PJ
 

Reply to HELP !!! RCD Mystery in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

An RCD keeps tripping. Please see attached photo of the board (2 photos attached). I’ll call the breakers: MCB (1) marked ‘Upstairs lighting’...
Replies
4
Views
996
I'm writing this mainly hoping something occurs to me while writing it! I got called to an occasionally tripping RCD. It's a Hager double height...
Replies
19
Views
2K
I have just checked a double outlet and it trips at 18ma. It was supposed to be faulty. Washing machine had a bad heater which got replaced but...
Replies
10
Views
542
Hi all, There's 2 single fan ovens in the house my mother recently moved into. Posh elecronic AEG units. It's been sat empty for a year, so the...
Replies
19
Views
1K
Hi, I swapped a 2 gang switched socket for a 2 gang switchless socket with usb ports downstairs. I switched off all the power to the house by...
Replies
8
Views
756

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock