I would greatly appreciate if someone could help me understand the following outcomes on an EICR. I am being advised it needs a total rewire but I am a layman.

The wiring is approx 30. Years old. 4 circuits, 2 x lights, one mains (incl kitchen), one for living room.

We will be renovating the ground floor of the property including the kitchen.

Observations
  • no RCD protection to any circuit (C2)
  • Damage to electrical wiring accessories (C2)
  • Burnt connections in the back of kitchen sockets (possible cause of overloading or loose connections) (C2)
  • immersion heater has been rewired on the same circuit as the sockets - risk of overloading (C2)
  • no CPC continuity to circuit 2 ring main (F1)
  • unable to locate water bonding (F1)
  • no smoke alarms (C3)
  • no surge protection fitted to consumer unit (C3)

The sections of the report on the EICR as C2 are
  • 4.13
  • 4.17
  • 4.18
  • 5.3
  • 5.5
  • 5.12
  • 5.18
  • 6.1

Thank you
 
Can you post the whole report here, but remove the name of the company that did the inspection?
There's a best-practise guide from electrical safety first called best practise guide 4 that is worth you acquiring.

Generally wiring from 30 years ago would normally be in serviceable condition. The full report should help us gain a better picture. The reasons for requiring a rewire are usually
a) dangerous wiring that is at end of life or has been damaged. Some of the tests on the report will help determine this
b) not enough points in the right places or not enough circuits to cope with modern demands
c) revonations are happening and it's a good opportunity

Quick thoughts about the other items:
  • no RCD protection to any circuit (C2) See Best Practise Guide 4
  • Damage to electrical wiring accessories (C2) Not expensive to replace
  • Burnt connections in the back of kitchen sockets (possible cause of overloading or loose connections) (C2) If the wiring is serviceable the accessories can be changed.
  • immersion heater has been rewired on the same circuit as the sockets - risk of overloading (C2) This is a reasonable comment in my view.
  • no CPC continuity to circuit 2 ring main (F1) This should be a C2, FI would be for if he couldn't complete the test. This needs sorting out.
  • unable to locate water bonding (F1) The water pipes can be tested to see if it is likely they are bonded.
  • no smoke alarms (C3) This should be a NOTE as it doesn't relate to electrical safety.
  • no surge protection fitted to consumer unit (C3) Fair enough
 
Can you post the whole report here, but remove the name of the company that did the inspection?
There's a best-practise guide from electrical safety first called best practise guide 4 that is worth you acquiring.

Generally wiring from 30 years ago would normally be in serviceable condition. The full report should help us gain a better picture. The reasons for requiring a rewire are usually
a) dangerous wiring that is at end of life or has been damaged. Some of the tests on the report will help determine this
b) not enough points in the right places or not enough circuits to cope with modern demands
c) revonations are happening and it's a good opportunity

Quick thoughts about the other items:
Thank you - I attach the report below.
 

Attachments

  • F553ADA8-B22E-46CE-A201-0262E54FBC9E.jpeg
    264.6 KB · Views: 86
  • B9E87560-FDB1-446F-8E47-441FD19BF2F9.jpeg
    254.7 KB · Views: 67
  • F0CC31F7-877A-45BE-BB5F-BEE226D10C34.jpeg
    435.9 KB · Views: 66
  • 468DE5DE-4341-4C63-9649-6A01F1F99435.jpeg
    716.5 KB · Views: 59
  • FD3B11CA-28C3-4F64-8B9D-F3BC39E7FB36.jpeg
    833.5 KB · Views: 43
  • DD6387DA-E6E2-4BC6-B762-F555125BDE32.jpeg
    581.4 KB · Views: 75
Hmmm. Well he can't have it both ways - his test results actually portray the fixed wiring as being in excellent condition. (The insulation resistance tests for all circuits are all >200M.). If the overall condition is as bad as he says I'd be very surprised to get those readings. The discrepancy between the overall comments and the test results make me wonder if those tests actually happened or the readings were invented.

I also noticed 4.17 - RCD's required for fault protection. This should not be a C2. Fault protection is covered by other methods on your installation and the tests results show it will work. I worry when I see this as it doesn't build confidence.

Also, he's listed type AC RCD protection for each circuit. This is very confusing.

So far, at a minimum and obviously without seeing it I'd be saying that
-the upstairs socket circuit needs fixing
-some accessories may need changing
-a new circuit should be run for the immersion heater
I'd also be advising a new consumer unit is installed but that doesn't mean what is there isn't safe. It's just that modern units do lots more to protect people from the dangers of electricity.

Additionally the insulation resistance results need confirming (ideally by someone else) as you are relying on them to know whether the opportunity should be seized to get some new cables in. This is really the most important thing. If we believe those results I'd struggle to justify a rewire for safety reasons.

As I already wrote - it might be that your intended use of the property means there are insufficient points and a rewire would be a good idea for other reasons.
 
Thank you - all advice greatly appreciated. The intended power points are adequate for what we need.
We will be fitting a new kitchen - would that change anything? Apologies I am a complete novice.
Attached the consumer unit (aware this needs replacing as a minimum)
 

Attachments

  • 77DB5249-C364-4F71-A19F-4AA545ACFAA6.jpeg
    956 KB · Views: 78
Hmmm. Well he can't have it both ways - his test results actually portray the fixed wiring as being in excellent condition. (The insulation resistance tests for all circuits are all >200M.). If the overall condition is as bad as he says I'd be very surprised to get those readings. The discrepancy between the overall comments and the test results make me wonder if those tests actually happened or the readings were invented.

I also noticed 4.17 - RCD's required for fault protection. This should not be a C2. Fault protection is covered by other methods on your installation and the tests results show it will work. I worry when I see this as it doesn't build confidence.

Also, he's listed type AC RCD protection for each circuit. This is very confusing.

So far, at a minimum and obviously without seeing it I'd be saying that
-the upstairs socket circuit needs fixing
-some accessories may need changing
-a new circuit should be run for the immersion heater
I'd also be advising a new consumer unit is installed but that doesn't mean what is there isn't safe. It's just that modern units do lots more to protect people from the dangers of electricity.

Additionally the insulation resistance results need confirming (ideally by someone else) as you are relying on them to know whether the opportunity should be seized to get some new cables in. This is really the most important thing. If we believe those results I'd struggle to justify a rewire for safety reasons.

As I already wrote - it might be that your intended use of the property means there are insufficient points and a rewire would be a good idea for other reasons.
Thank you - in terms of estimated costs (or is it a case of how long is a piece of string) would you expect?
 
his test results actually portray the fixed wiring as being in excellent condition. (The insulation resistance tests for all circuits are all >200M.). If the overall condition is as bad as he says I'd be very surprised to get those readings.

I don't agree, the test results show that the wiring has good IR, this doesn't necessarily imply the wiring being in excellent condition.

You could have ununeclosed connector blocks everywhere and still get a good IR.

Even bare exposed conductors will show a good IR if theres a couple of mm free air between them.
 
I don't agree, the test results show that the wiring has good IR, this doesn't necessarily imply the wiring being in excellent condition.
All we have is "The installation is old and requires improvement" and little else to go on.
Maybe I over stated it but my point is if the issue is age related (as per the comment) then I'd usually expect some signs of deterioration in the IR results.
You could have ununeclosed connector blocks everywhere and still get a good IR.
Even bare exposed conductors will show a good IR if theres a couple of mm free air between them.
Sure but there's no C1's and no mention of anything suggesting any of this.
I do take your point that saying "excellent condition" is too strong, I was really trying to highlight a discrepancy.
 
Apologies if I haven’t been clear - this is for a house purchase which is in process. We know there is upgrading work to be done on the electrics - the electrician who carried out the EICR has been vague beyond ‘yes yes it has failed and needs a rewire’. We are paying this cost and not using it to negotiate with the seller. But are trying to understand if it is a true rewire or just upgrading. As it would change our approach on moving in straight away or getting the rewire done.
Appreciate all the responses given!
 

Reply to Help Understanding EICR in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Good day. First time poster. We recently had an electrician perform the EICR, as this is a newly purchased property I thought'd I would have the...
Replies
7
Views
692
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Been asked to do remedials on holiday cottages after recent EICR. Modern consumer units, MK Sentry, but no RCD protection on anything. Bit of a...
Replies
13
Views
2K
All - Would appreciate some advise or professional help as I'm facing a £4.5K bill following an EICR which seems to highlight issues that passed...
Replies
21
Views
4K
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock