Hello can anyone please help as im new to this but always researching to better my knowledge. Im trying to identify the BS info for the msin switch. I know the fuses are BS 3036. Any help would be appreciated. Thanks20170726_123413.jpg

20170726_123413.jpg
 
BS5419, you will have to record its current rating as n/v as it could be 60 or 100A but it is likely to be 60A.
 
Assuming it is missing you should note the fuse cover is not in place, with current requirements you could argue it maintains some IP rating but its original purpose was to prevent molten copper being emitted if one of the semi enclosed fuse wires ruptured.
 
Don't forget to use the 0.725 correction factor on the 3036 fuses for current carrying capacity of the connected conductors.
 
The 5 amp circuit no 2 looks like a cartridge fuse possibly bs 1361 or bs 88
You'll be able to take the carrier apart to confirm its type
 
BS1361 although you should always check it hasn't been linked out with wire or that someone has fitted a BS1362 plug top fuse, even though longer they will fit but it splays the blades.
 
BS1361 although you should always check it hasn't been linked out with wire or that someone has fitted a BS1362 plug top fuse, even though longer they will fit but it splays the blades.
Ha I've seen the old plug top fuse rammed in before.
Tenant said he had an abundance of 13amp fuses he's carried for years, straight into a 5amp cartridge holder for lighting.
What could possibly go wrong?
 
I suppose BS88 could be correct if you use the new categorisation of BS1361 being BS88-3 fuse System C, madness.
 

Reply to Help with identifing main switch type. New to periodic testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
598
Hi guys. I posted yesterday about a suspected faulty starter motor.. I've had the starter out and cleaned everything up and all seems to be...
Replies
6
Views
729
D
Hi, I have received conflicting advice about Main Isolator Switches and would appreciate forum member's help to plan a way ahead. Looking to the...
Replies
5
Views
2K
Deleted member 155212
D
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
504
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock