Ive a couple of queries about the AM2. Having tried twice now I failed the c1 safe isolation and even failed part of it that I passed the first time doing the same thing. When isolating the luminaire o the 3 phase board I asked permission then opened the breaker and locked it with a sign on and put the key away. I took the board cover off and proved the test meter then checked L-N, L- E and N-E then reproved ithe meter. Then I replaced the board cover and used the step provided to remove the luminaire cover. Proved the test meter and checked L, N E at the fitting in the same sequence as before and with each wall switch in a different position the reproved. I replaced the luminaire cover. I did the same for the 3phase DOL starter but using the 10step sequence for testing and by replacing covers on the board in the same way. To isolate the whole board I did the same but just one the main breaker using the 10step sequence then replaced the cover. I aslo failed the instal on the data section. I fitted it all but when testing began I realised line 1 and 6 didnt light up the meter. I redid both and they didnt work and redid them again after getti g line 1 to light up but not 6. I asked the examinor who did the same and then said the face plate was faulty so not to worry about it and he would note that on the exam notes so i left it as he instructed. Any ideas? Cheers
 
" Light up the metre", not sure what you mean, were you not using a recognised voltage indicator? plus proving unit
 
Hi,

From what you have written you seem to have taken off the db cover during safe isolation on the lighting & dol? Is that correct.

When isolating the lighting circuit for example:

Identify the correct circuit
Ask permission
Lock off + warning labels & key in pocket
Check AVI as per GS38
Prove AVI
Carry out dead tests at light accessory dont forget to do all the swiches positions so you test the strappers.
Then redo the dead tests again at the switches
Reprove AVI

No need to take db cover off.
 
" Light up the metre", not sure what you mean, were you not using a recognised voltage indicator? plus proving unit
They provided a data cable test meter for that bit with the cycle of 8 lights to show the cable is fully connected. Each number from 1-8 lights up to show the connection is true.
[automerge]1576781429[/automerge]
Hi,

From what you have written you seem to have taken off the db cover during safe isolation on the lighting & dol? Is that correct.

When isolating the lighting circuit for example:

Identify the correct circuit
Ask permission
Lock off + warning labels & key in pocket
Check AVI as per GS38
Prove AVI
Carry out dead tests at light accessory dont forget to do all the swiches positions so you test the strappers.
Then redo the dead tests again at the switches
Reprove AVI

No need to take db cover off.
Hi, thanks for replying. I thought that was the case but asked soneone I know who trains peolle for the am2 and he told me to take the db cover off and replace it before testing the light too
So i dont do that bit then. For the whole 3phase i did that so how would that fail as I couldnt test it without removing the cover? Ta
 
They provided a data cable test meter for that bit with the cycle of 8 lights to show the cable is fully connected. Each number from 1-8 lights up to show the connection is true.
[automerge]1576781429[/automerge]

Hi, thanks for replying. I thought that was the case but asked soneone I know who trains peolle for the am2 and he told me to take the db cover off and replace it before testing the light too
So i dont do that bit then. For the whole 3phase i did that so how would that fail as I couldnt test it without removing the cover? Ta
Don't make any sense Mate sorry
 
They provided a data cable test meter for that bit with the cycle of 8 lights to show the cable is fully connected. Each number from 1-8 lights up to show the connection is true.
[automerge]1576781429[/automerge]

Hi, thanks for replying. I thought that was the case but asked soneone I know who trains peolle for the am2 and he told me to take the db cover off and replace it before testing the light too
So i dont do that bit then. For the whole 3phase i did that so how would that fail as I couldnt test it without removing the cover? Ta

When your doing safe isolation in the AM2 for the lighting & dol circuit your doing this for ie maintenance purposes. Ie so you could change the light or dol starter. This covers both single phase & 3 phase.

When asked to isolate the db you will need to do your safe isolation procedure & you will need to take the db cover off to do your tests. This covers for example maintenance work in the db ie adding new circuits etc.
 
When your doing safe isolation in the AM2 for the lighting & dol circuit your doing this for ie maintenance purposes. Ie so you could change the light or dol starter. This covers both single phase & 3 phase.

When asked to isolate the db you will need to do your safe isolation procedure & you will need to take the db cover off to do your tests. This covers for example maintenance work in the db ie adding new circuits etc.
Cheers. can i just double check one more thing you said. Once you have tested the light fitting you remove the face plate from each switch (2 & an intermediate) and test them one at a time too in the same way. Then you're done?
 
Cheers. can i just double check one more thing you said. Once you have tested the light fitting you remove the face plate from each switch (2 & an intermediate) and test them one at a time too in the same way. Then you're done?

Yes but remember to reprove AVI to confirm that it's still working
 
Stupid question; where did you put the key?
Ah yeah I forgot to add that in my post. It was in my pocket for each one. I reckon it was removing the db cover that failed me despite getting advice beforehand to do that and for the final 3phase im not sure as I did everything as far as i remember.
 
Seems kinda odd that they don't tell you what you failed on ? Is it supposed to be a secret ?
Its a very closed exam. You get a printout showing which sections you fail but no detail. They said you coud ring for feedback but it wouldnt include any detail. Given that section is 8.5 hours long and costs hundreds of pounds I think they should give you more information but maybe thats just me. 40% pass rate at nearly £700 a go...
 

Reply to Hi all, in the Electrician Courses : Electrical Quals area at ElectriciansForums.net

Similar Threads

resitting Saturday my am2 4 sections a3/b/d/e swa and sy failed on protective conductors on both swa i under stand thats the earths i...
Replies
1
Views
1K
A BG fused connection unit, with neon. A boiler. Fuse out. Spur switched off. I was checking polarity after a colleague had 2nd fixed it and...
Replies
7
Views
710
Hi all, hoping for some advice, I’ve recent resit my AM2s after failing on first attempt… I’ve passed all my resit apart from section C just on...
Replies
0
Views
818
I've been installing Type 2 SPDs in consumer units for several years now, and they always come as a pair, connected across L & E, and across N &...
Replies
2
Views
504
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Replies
2
Views
537

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock