Discuss Hi, can anyone offer any advice as to why the heating would run when HW is called for? in the Central Heating Systems area at ElectriciansForums.net
Hi thanks for your message. There is not a valve on this system. It looks like it uses the double pole relay, It is a very old system. 1978 it was installed
Surely there still has to be some sort of a motorised valve to close the heating circuit. If not then you will always have heating when the boiler fires.
Based on the wiring center diagram you've posted you have a conventional system boiler.
You will have one, two (or even 3) zone valves as per the pictures bellow.
No, the wiring diagram posted does not show a conventional system boiler with zone valves.
The wiring diagram posted shows a 2 pump system utilising a DPDT relay. The biggest clue to this is 'two pump system' written on it.
[automerge]1596964186[/automerge]
According to the picture it is a two pump system, no motorised valves are used with this.
[automerge]1596964649[/automerge]
It is impossible to say from just that diagram.
Haa it always worked this way or is it a fault which has developed recently?
Does the room thermostat have any effect when the CH has come on via the hot water controls?
Unfortunately the wiring diagram is incomplete, it doesn't show the internal links between the connections so we can only guess at what the full circuit is.
Without further information this needs to be tested by a good electrician.
I apologies, your right, I didn't look closely enough at the diagram to see the second pump. I didn't even know such a system existed, I've seen gravity hot water but never a second pump.
Surely without a valve both systems will always heat up?
[automerge]1596964910[/automerge]
If there are no valves in the system a blockage in the hot water flow/return may well force flow through the heating circuit instead.
No, or not to any significant extent. With one pump running and the other not the vast majority, if not all, of the hot water will be circulated by the running pump and not get through the stationary pump. This assumes the system is properly designed.
There is a possibility of heat creeping via the return pipe, but good pipework design should combat this, or a non return valve.
[automerge]1596965220[/automerge]
I doubt that this would cause enough flow through the heating to make it appear to be on, maybe slightly warm at best.
A blockage in the hot water pipework will cause the hot water pump to be pumping against the blockage, this won't normally cause any water to flow via the heating pump.
This is the old wiring centre, we assume it has always worked correctly. Please not that on the picture if there is a notch then the terminals have a link. We have rewired the property but kept the heating system as was just renewing the cabling. Could the frost stat cause an issue if set to call for heat?
Ah, so you are an electrician working on the system, your OP gave the impression of a fault finding situation on an existing installation, not that you'd interfered with the wiring and messed it up.
My first question has got to be why did you mess with a working system?
Did you not take the time to investigate and understand the control system before you took it apart?
Did you test the system before taking it apart to ensure you understand how it is supposed to work and whether or not it was working correctly?
You have the old wiring centre and the wiring diagram so you can work backwards from this to draw yourself a diagram of how it was connected previously. From this you can work out how the system is supposed to work and then start to fault find.
[automerge]1596969169[/automerge]
Do you have a diagram of exactly how you have connected the new wiring for this system?
Without that the most we could possibly do is draw a diagram of how it was originally wired, but that won't help explain why it is not working now.
Thanks for your message.
My mistake was not confirming how the system worked and if it worked correctly. We had to rewire the system as all cabling did not have any cpc's and the original install was installed very poorly. I have done as you suggest and worked backwards and cannot see any immediate issue with the design of the system. Hence I am looking for another input from electricians. Thanks for taking time to reply to this thread. I assume you don't have any advice as requested ?
Do the pumps stop and start in response to demand from the two thermostats/time clock?
If you connect a switched live to the boiler and temporarily connect power the pump bypassing the controls does the issue go away?
If you fire the boiler and run only one pump and the other circuit heats up that would imply its a piping design/plumbing fault rather then a an electrical issue.
Heating systems used to be entirely gravity fed using only the fact cold water is more dense than hot water. It may be your getting effects such as these.
Thanks for your message. I am back on the job tomorrow. I will what you have suggested ?
So can you post the wiring diagram you have created of the old system? Or describe its operation?
Can you also post the wiring diagram of what you have installed?
You haven't given enough information to be able to offer any helpful advice as far as I can see.
A diagram of what you have installed will allow us to see how it is currently operating and suggest how to achieve the desired operation.
I have given all the advice I can confidently give without further information.
I could offer you a bunch of random guesses at what might be wrong, but that wouldn't help.
I am back on site tomorrow Dave, I will see what is happening and if unable to resolve I will send a diagram of the installed system. Thanks for your message
Reply to Hi, can anyone offer any advice as to why the heating would run when HW is called for? in the Central Heating Systems area at ElectriciansForums.net
  • Locked
Hi, I realise this is an electrical forum and not plumbing, but was wondering if somebody could help. My heating is not working and the heating...
4K
(Or that might be should a failed HW valve keep boiler running) Woke up this morning to find the boiler still running even though all timers off...
Hi Guys Changing my heating/water programmer and im stuck on the wiring ive gone from a danfoss to a Drayton and the wiring description is...
I'm in Raleigh, North Carolina and have a well for my house's water supply. For some reason, pitless adapters, which allow all piping to be run...
I have a fully pumped Y plan heating system using a Potterton EP2 programmer. Drayton MA1 Diverter valve. I have just replaced the Actuator head...