Hi
I'm after some advise on electric underfloor heating?

I've recently taken over a job were the previous electrician (kitchen fitter) has left the job half done and left them with an unfinished job mainly all 2nd fix

He's laid 2x 20m matts to cover a 40sqm room and he's put 1 prob and Both tails from each matt to a 35mm box with a supply from a dedicated circuit which was isolated by a 20amp double pole switch the two matts will be controlled by one thermostat rated at 16amps. from what I have found out through the customer is that the Matt rating was 200wpm so by my calculation
40x200 = 8kw /230 = 34.78amps.

So 34.78 amps into 16amp thermostat?
What's my solutions?

I've had a quick read up about contactors ,relays and snubs to be honest I have never used any of these so not sure on were and how to wire them into the circuit.

This install is completely plastered/decorated so re-wiring or major changes to the circuit can't be done unless local to existing wiring

After any helpful advise

Cheers
 
what lunatic specified electric underfloor heating for a room that size. madness. something close to £100 / week in leccy.
 
what lunatic specified electric underfloor heating for a room that size. madness. something close to £100 / week in leccy.

They were sold it as part of the kitchen install I had a rough measure up and you could of got away with 0ne 20m Matt after you minus all the fixtures and fittings the Matt goes under all the units
 
Use the stat to switch a contactor, this may have been the original intention.
What type of contactor would be needed?
And can you get small contactors that would fit inside a 35mm box?

In my mind I would have a feed from the stat to a contactor and the cold tails to the contactor aswell?
 

Reply to Hi,new to the forum after advise and willing to learn Thanks in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hi all looking for some advice as a non sparky , be gentle :) To be clear I wont be doing the work myself , just want to be better informed. I...
Replies
7
Views
2K
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Hello everyone, I must admit I'm kind of terrible when it comes to introductions so here goes whatever I can put together. Name's there, just like...
Replies
3
Views
1K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock