Hi all.

quick question, on a rfc wires in 2.5 single or tne, can you use high integrity sockets and terminate each cpc into a different terminal, and same at the db, or do you have to pull a 4mm radial cpc
in aswell.

i learnt that you could just split the cpc at college years ago, but reading up it apparently needs to be 4mm?

also what would you code a computer circuit with no high integrity earthing on a eicr?
 
Hi all.

quick question, on a rfc wires in 2.5 single or tne, can you use high integrity sockets and terminate each cpc into a different terminal, and same at the db, or do you have to pull a 4mm radial cpc
in aswell.

i learnt that you could just split the cpc at college years ago, but reading up it apparently needs to be 4mm?

also what would you code a computer circuit with no high integrity earthing on a eicr?

Is the protective conductor current likely to exceed 10ma?
 
Figure 7.5.3 ON site guide mate. One terminal to be used for each protective conductor including at the DB (obviously a Ring final). The CPC must have a minimum csa of 1.5mm with the circuits marked at the DB indicating high protective conductor currents.
 
Cheers everyone. But thought it would be more than a c3, as a disconnected cpc could lead to the cpc having half the potential of nominal voltage?
 
Hi all.

quick question, on a rfc wires in 2.5 single or tne, can you use high integrity sockets and terminate each cpc into a different terminal, and same at the db, or do you have to pull a 4mm radial cpc
in aswell.

i learnt that you could just split the cpc at college years ago, but reading up it apparently needs to be 4mm?

also what would you code a computer circuit with no high integrity earthing on a eicr?

I will need to have one of my rare visits to that good book to see if I am about to state a load of bull

The total area of all the conductors in a multi core cable inc the live conductors shall be not less than 10mm

If that is correct then there will be no code for a twin+E ring final even if its used without the sepearate 4mm earth as per a radial
 

Reply to High integrity earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
Hi All Seen this on a few jobs now where they have on the Downlight fittings where the CPC is terminated outside the enclosure of the Downlight...
Replies
55
Views
5K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi, I have a dual RCD board made by Hager installed a couple of months ago. It is high integrity, which I understand to mean RCBO’s can be...
Replies
17
Views
3K
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
769

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock