Farmelectrics

-
Arms
Reaction score
520
In the office building were we are doing 5 year eicr s I've come across this under the floor are bus bar power tracks supplying various power points under floor and to desk top pcs so the maintenance guy on site tells me the pcs are plugged in to the red sockets because they have 2 earths in fot high integ earthing and the power under floor goes into the white ones but supplying the bus bar tracks is a 3 core 16mm swa so we have one earth back in db so how have they achieved high integrity earthing bit confused
 
As long as the swa earth tails are into separate earth terminals then it still follows the practices for high integrity earthing.
 
Desk top PCs often have a small leakage to earth from the internal power supply unit. This can be as much as 5 mA. Here in France we put red sockets in offices &c especially for these to indicate that they are on a circuit which is NOT behind a 30 mA RCD -- since if you have 6 desk tops you may have 30 mA leakage - which will trip out. In industry in the UK - as far as I know, computer equipment supplies are specialized and not put behind a 30 mA RCD for the same reasons. Don't know if this is any help :)


I found this on this forum .... http://www.electriciansforums.co.uk...-computer-sockets-high-integrity-earthing.pdf
 
Last edited by a moderator:
Desk top PCs often have a small leakage to earth from the internal power supply unit. This can be as much as 5 mA. Here in France we put red sockets in offices &c especially for these to indicate that they are on a circuit which is NOT behind a 30 mA RCD -- since if you have 6 desk tops you may have 30 mA leakage - which will trip out. In industry in the UK - as far as I know, computer equipment supplies are specialized and not put behind a 30 mA RCD for the same reasons. Don't know if this is any help :)


I found this on this forum .... http://www.electriciansforums.co.uk...-computer-sockets-high-integrity-earthing.pdf

A standard RCD will trip anyway from 50% to 100% of its rating this we have a 3mA per computer benchmark so usually max 4-5 units, you can fit SI units that recognise the frequencies of the earth leakage created by designed leakage and these SI units ignore this and only trip on fault leakage these allow many more stations per circuit.
 
The SI (Hi Haute immunité ) RCD would still be used only for the Computer circuits - so the sockets here would still be distinguished by being red..... The 3 mA benchmark is closer to the 3,5mA limit than the 5 mA - but since I would not (cannot) use a ring here and have to limit the number of outlets to 8 Double sockets per MCB protected spur - It is easier to excuse the considerable extra cost of the SI/Hi RCD.:wink5: Er ... I think we are actually agreeing - but I am not sure we are helping with the original question, which I think you had already answered above - now that I understand it. :smile5: Sorry :yes:
 
Last edited by a moderator:
Ok in reply to using the armour as part of the earthing the cable gland is glanced into the db but still there is only one eart of the swa in the earth bar so were have they achieved high integrity earthing
 
Ok in reply to using the armour as part of the earthing the cable gland is glanced into the db but still there is only one eart of the swa in the earth bar so were have they achieved high integrity earthing

To meet BS7671 the swa at the dist-board is required to be tailed from the Banjo to the earth-bar, as this is high integrity the BS7671 requires separate terminals to be used for each earth, as you have 2 earth conductors now in the board they should enter separate terminals and appropriate label fitted warning of the high integrity earth and what circuit involved. It can be argued that the gland on the enclosure provides separate contact but that may have been the case many years ago but earth tail now required.
 
Well on the next inspection it needs noting as its a mechanical thing and requires separate termination just in case a lose earth terminal exists it has a functional alternative path to take current away ....if the doubled up earth terminal came loose in the board the high integrity earth is lost and users may be getting shocks off the computers etc ...a dangerous set-up.
 
The requirements for high integrity earthing can be met by a number of methods, multiple protective conductors are not the only option, a single conductors of sufficient cross-sectional area can also meet the requirement.

The Electrak busbars meet the requirement as they at 13mm sq. A single conductor in a 3core SWA cable with 4mm sq conductors will also meet the requirement. (Requirement is 10mm sq or 4mm sq with mechanical protection). If the SWA cores are 2.5mm you would then need to use the armour as a duplicate protective conductor.

I expect the SWA cores will be 4mm sq.
 
To meet BS7671 the swa at the dist-board is required to be tailed from the Banjo to the earth-bar, as this is high integrity the BS7671 requires separate terminals to be used for each earth, as you have 2 earth conductors now in the board they should enter separate terminals and appropriate label fitted warning of the high integrity earth and what circuit involved. It can be argued that the gland on the enclosure provides separate contact but that may have been the case many years ago but earth tail now required.


Well we didn't have any problem before they started supplying Banjo's with SWA gland termination kits!! But then that was in a time when SWA cables were all virtually made off correctly and solidly!! Can't really say that today, not with some of the abortions we've seen in posted photo's on here recently!! lol!!
 
Well we didn't have any problem before they started supplying Banjo's with SWA gland termination kits!! But then that was in a time when SWA cables were all virtually made off correctly and solidly!! Can't really say that today, not with some of the abortions we've seen in posted photo's on here recently!! lol!!

What like this?...
 

Attachments

  • uploadfromtaptalk1375964736969.jpg
    59.9 KB · Views: 27
  • uploadfromtaptalk1375964761413.jpg
    38.9 KB · Views: 24

Reply to High integrity earthing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

2nd fixing some sockets in an office today and we were talking about high integrity earthing, I've not got a clue what the sockets are going to...
Replies
9
Views
1K
We have a customer in a large office block with all power in the building fed from an Electrak plug in busbar system. Lots of desks, lots of...
Replies
1
Views
228
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
Replies
11
Views
951
I'm in a questions asking mood tonight. I briefely looked at a job today and I need to recommend a board change but need to justify it. Firstly...
Replies
7
Views
1K
Hi was recently at a property and was installing a Solar PV system. was doing my testing and i came across a weird result when doing the...
Replies
23
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock