I’ve just been to look at a job where the client wants to have a couple of extra sockets fitted.
The consumer unit is an old rewirable with no rcd protection, but there is a new garage rcd/mcb board fitted next to it with a spare way that was installed just 2 weeks ago by their landlords electrician when he installed an electric heater.
Ok, should be easy, just test the existing circuit that I’m going to extend and put it into the new board on a 32 amp mcb.
The electrician only installed 16mm tails and 10mm earth but I can easily up grade these, the problem I have is that I did a quick Ze and got a very low reading of 0.04 ohms. This prompted me to do PFC test and I got a result of 11Ka.
Now, the new garage has domestic 6K breakers fitted, I know I can get 10K mcbs but I do not know of anything with a greater breaking capacity.
Any ideas ?
 
The 11 Ka is the maximum current that could flow in fault condition.
Therefore the breaking capacity of the mcb has to able to cope with this, this is why you note it on the certificate.
If the pfc was say 7Ka I would fit a 10Ka mcb, but as it's 11Ka even this would be inadequate.
 
I know this might be besides point now, but according to the OSG if you have a 11KA PFC, a 10KA breaker would be adequate, but would only be able to interupt a single fault before the breaker would be unusable. A 10KA would be able to keep in performance upto a 10KA fault, but after 10KA to 20KA should be able to perform once only.
Would like some confirmation on this, as this is something new ive learnt..:) or i think lol..
 
The rated short circuit current must be less than the pfc at the point where it is installed. OSG Pg 56.
The device is installed in the board, the pfc at the board is 11Ka.
 
yes but if there is a fault at the board the mcb is not protecting the board nor carrying the fault the device that protects the board (main cut outs) will do that and need to be 11ka or more if the fault is after the board the mcb will cover it but the pfc wont still be 11ka by this point

can anybody else confirm this is so.
 
Hey.

In relation to your Ze, your PFC should be around 5.8KA.

Your reading is a bit high, is the installation right next to a transformer/sub-station??
 
I know thats probably the reason the Ze is low which, in turn, increases PFC but 11ka is nearly double what it should be!

Possible faulty tester or leads??

Would be interested to see the readings for PEFC or PSCC.
 
The house is close to the sub station,
The Ze was what made me do a pfc test because it is a t-n-s supply and the earth is just a bit of 10mm connected to a clamp on the lead sheath, (I think the last electrician fitted this, it's not right but i'm not going to touch it)
I did the pfc test across live & neutral.
 
Thanks Lenny.
Back to my op, what can I do about it? and does anyone know of an mcb with a higher breaking capacity?
 
Andy,

Your PFC does sound very high indeed and calculation gives nearer 6ka.

Would your meter be giving a false reading?

I dont think there are any MCB's rated over 10ka, unless there may be some specialised manufacturers.
 
I know of no MCB above 10KA. Do you have a Fluke multifunction tester?? I've heard on the grapevine that these particular testers do have issues with fault current measurements.
 
Andy,

Your PFC does sound very high indeed and calculation gives nearer 6ka.

Would your meter be giving a false reading?

I dont think there are any MCB's rated over 10ka, unless there may be some specialised manufacturers.

Jason, what calculation have you used to get 6K?
 

Reply to High PFC in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock