Discuss high PSC? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Did some testing and my readings on 3 phase psc was like 6.7Ka, is that normal? as I find it rather high? thats between 2 of the phases, whats the reasons for this? and is it the suppliers fault for it being so high, What is an average PSC reading on a three phase and single phase anyway?
your reading can be high especially if your close to sub station
if it goes over max permissable for device(mccb) try bs88's as they have a higher Ka rating
Luke
NO NO NO NO
repeat after me
NEVER TEST PSCC BETWEEN PHASES
most test meters operate on 230V. You have just banged 400V accross it. Not good.
Measure PSCC Line to Neutral as you would with single phase, then double it to get your three phase value.
Dont forget your PFC's are just mathematical evaluations of Ze or Z.
I = V/R
where I is PFC and R is Z or Ze
so for a Ze of 0.5 ohms for example I would be PEFC would be 460A
If you were to measure Z (between line and neutral) and use this value, it would give you PSCC, which would then be doubled for a threr phase system
Most 60898's i have seen are rated at 10KA so you are fine
some meters DO test phase to phase (metrel if memory serves)
and your right dont test at 230 across 400 bang new meter please!!
Luke
NO NO NO NO
repeat after me
I = V/R
Most of AVO(MEGGER) you can test between phases go up to 440volts
Yes I agree Ian, some meters will, and some meters wont. And some people dont know the difference. So adopting the standard practice (as per GN3) of measuring phase to neutral and doubling the value to obtain equivalaent three phase value is a good deal in my book.
It GUARANTEES the meter aint gonna go pop!:eek:
pscc is done either with 3 leads or 2
if you are using 3 leads the black and green lead goes in the neutral and the red lead in the phases
take all 3 readings and then double the highest
if you look in guidance note 3 it say that in a 3 phase system the pscc will always be the higher than pefc because as a rule of thumb you double it
3-phase psc measurements aren't really that difficult. It strikes me that if you are live testing you should know how to use your instruments and know its limitations. (see GN3 for advice).
The old Robin loop testers will give you a firework display, without warning, if used to test 3-phase psc, but the newer Flukes, Meggers, and Metrels are usually Ok.
Reply to high PSC? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Hello all, I signed up here for a little help. I bought a 3 phase bandsaw and went down the rabbit hole of VFD’s etc. ‘The motor is 3 phase 400v...
Evening all, I have a little conundrum I need to get resolved. I’ve moved an EV charger from a single phase board that was on a 40a breaker and...
Hi all, any advice would be greatly appreciated. Went to do some work at a factory unit on Monday ( changed 20 florries to LED battens and changed...