Hi all new to this so hopefully i can borrow some wisdom. I am currently carrying out a periodic inspection and testing of a commercial property. I have a db with 40 of the same circuits. The circuit is a 6mm radial to a junction box then a 2.5mm ring for 20 sockets. The circuit is wired in 6mm singles radial then 2.5mm singles in a ring. This is protected by a 40a RCBO 30ma type c. I am getting readings of around 1.20 for my R1 & R2 readings. This is the same for all these circuits. Connections are all tight inside sockets. How can i lower the readings to allow me to keep the same size of RCBO.

Thanks in advance.
 
Regardless of the reason of the readings that is another topic, just to chuck a grenade in, and just to point out that 1.20 is fine for a RCBO if a zs, can't imagine it being much more for a R1+R2, because it is an RCD I suspect it will be fine, and anything under 100 ohms ZS wise, will keep the NICEIC happy, under 200 ohms the regs and 1667 will confirm it trips with in the required disconnection time lol, and why consider changing the size of the RCBO????
 
Last edited by a moderator:
I am testing R1 & r2 by connecting the earth and live at the db and testinbg on ohms at the sockets (furthest point). My Ze is 0.09 and my zs readings were roughly between 0.20 and 0.35. The RCBO's are tripping in time for x1 and x5. I may be wrong but i thought these R1 & r2 readings were high. Apologies if this is not the case.
 
My point is if the ZS readings are that low 0.20-0.35 and is covered by RCD and it isn't tripping then so what, actually the circuit may have some cable length hence the reading, so zs = R1& R2 plus ZE

ZS-0.09
R1&R2 1.20
ZE= 0.35

????
 
I am testing R1 & r2 by connecting the earth and live at the db and testinbg on ohms at the sockets (furthest point). My Ze is 0.09 and my zs readings were roughly between 0.20 and 0.35. The RCBO's are tripping in time for x1 and x5. I may be wrong but i thought these R1 & r2 readings were high. Apologies if this is not the case.


Have you taken any sockets off and tested on the terminals?
 
Yes i tested on socket terminals for my readings. Also checked connections were tight when i thought the readings were high. I think i may have thought the readings were high when it doesnt matter judging by the above posts.
 
My ze for the db was 0.09 tested with main earth disconnected. My zs for the circuits was varied between 0.20 to 0.35.
To determin the ZE at the board, you would need to test the main earth and disconnect all other Earthing and Bonding conductors to avoid parallel path readings.
 
I was just reading what you wrote in an earlier post


ZS-0.09

R1&R2 1.20
ZE= 0.35


Was not sure if you had mixed up Zs with Ze reading thats all.
LOL, yes I did mix up the readings chuckle, still interested in how he obtained the reading, although 0.09 sound good if it is a TNC-S system in any case.
 

Reply to High R1&R2 readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
  • Question
Hi - Just joined the forum as I'm making a career change and am training up. I've come across some mock papers online and am concerned that...
Replies
7
Views
331
Hi All Happy new year to all! First post but long timer lurker, so thanks for all the previous help! Just wanted to clarify something I have...
Replies
7
Views
810
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock