Discuss High R1 + R2 Readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
K
kduck
Hi,
Just taken these readings on a ring final
R1+R2
at the sockets
1 0.67
2 0.67
3 0.70
4 0.71
5 0.70
6 0.70
7 0.81 Spur
8 0.67
9 0.75
10 0.77
11 0.91 spur
12 0.71
Ze = 0.26 and Zs = 0.57
so all ready the sockets on R1+ R2 are all more than Zs any ideas
Insulation test L / N 77
E / L 84
E/ N 81
Also taken cooker reading, one 10mm wire running 9m, R1+ R2= 1.25 Zs = 0.75
meter was tested this week
help
what are the sockets wired in if 2.5 twin and cpc under the floor if so they are high readings, have you followed the test procedure ie: end to end first that way you should find out if you have problem with one or more of the wires
Harvey
took the readings end to end, also zero the leads. The house is a large one and all the sockets where on the same circuit up and downstairs plus the garage. So to get the readings down the easy option was to put the kitchen on it own ring, now R1 + R2 max is 0.07 in the kitchen and 0.10 on the socket circuit.
That was it all the sockets on one cct also probably over a 100m of cable hence high if you break them down even more 1st floor on one and ground on another is that possible ?
I think 100m ring length is right in for the 16th. I don't have my book handy but i think it is now 92m in the 17th edition. Not certain but pretty sure.
My rule of thumb is never use anywhere near a full roll of cable for a circuit.
Reply to High R1 + R2 Readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Slightly strange one this, replaced a few socket fronts in a dining room today, all wiring original but new plasterboard on a studded wall. Its a...
Domestic house, ring final circuit on an rcbo, end to end tests: r1 = 0.95 ohms, rn = 0.98 ohms, r2 = 1.02 ohms. It's rare a reading is too...
Hi guys looking for some guidance ,i am assisting with the renovation of an old building that contains a commercial kitchen and restaurant the...