GT1

I'll be pulling the circuit apart anyway..
However, Thought Id run it past the forum before I do.
Been testing today prior to CU change soon.
When testing one of the 2 RFC's at the house all was going well, until i got very high readings at about 4/5 of the socket outlets upstairs.
I was testing for my final R1+R2 figure. I was cross connected as required at the board.
The first few sockets were coming back around 0.45 or so.
Then I started getting readings at 50 ohms...?

The curious thing is, the end to end readings (r1, r2, rn) for the circuit were fine, well below 1 ohm and all as expected..
If i had a poor/loose connection somewhere then I would have thought it would have shown on the end to end readings too..?

The high readings are all quite close to each other, within 4/5 ohms..

As I said I'll be pulling it apart anyway, just wondered if anyone had experienced similar..?

cheers.
GT
 
Last edited by a moderator:
yes well its been modified over the years. It was originally an upstairs ring but its been extended downstairs into the kitchen for several sockets..!
Its mainly the end to end readings being normal that's thrown me.
 
Are you plugging in to the sockets to get readings? If so, try pushing the plug in and out a few times to "clean" the contacts which the pins touch. I have had it before where little used sockets have had dirty pins.
Or try unscrewing the fronts and use probes to check your readings.
 
thanks murdoch.. tried that but no change.. and one of the high readings is at a brand new (6 months old) socket..!
 
It is just old worn sockets. I do a lot of testing and a few things you find is the right hand side of a double is generally higher reading than the left as this is the side most people use first, just try flicking the switch on the socket a few times and that will bring it down usually if it doesn't the socket requires changing. Nothing more than wear and tear to the sockets
 
or is it a few sockets spurred off with a poor connection where they come off the RFC?
 
no single to double conversions and some of the sockets are brand new, some of them about ten years old.
Gave my plug in tester a good twist and a pull in each them too, without change..
The high readings are all on one side of the upstairs too..

My gut feeling is its a fault when additions have been done..
 
onions.. yeah im sure its not a spur problem either.. waaay to high for that.
Ive found spurs elsewhere on the job and theyre perfectly acceptable readings
 

Reply to high readings at (some) socket outlets in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi All, Had a weird one this morning during an EICR. Testing a ring final circuit in a 2 bed flat… kitchen was on a separate ring. With only the...
Replies
7
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
Hi Can anyone clear up or explain in a bit more detail what could potentially be causing the results I have. I have just tested a 32a ring main...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock