Discuss high voltage three wire to low voltage 4 wire? in the Electrical Engineering Chat area at ElectriciansForums.net
Think about how transformer windings are connected.
There are three types of connection Delta, Star and zigzag
Doing a sketch will help you work it out.
so the 3 wires coming in would be the higher voltage on the delta then would go through a transformer and come out as "star" providing an extra 4th wire (the neutral) ?
exactly. with delta ther is no neutral butonce converted to star via the transformer ( as the psecondary is connected as star) the star point is your neutral.
yes, the teory is too complex for a forum post, but basically. if the loads on all 3 phases are exactly balanced (equal), the the neutral current is zero. there is a formula for unbalanced loads.
N current = Square root of /(L1^2 + L2^2 + L3^2) - (L1*L2 + L1*L3 + L2*L3)
W
Would the star balance the load because of the neutral causing there to be a balanced load that the delta could take the ?
no. the balabce of the load on the star supply is determined by what loads are connected. you could have 110A on L1, 70A on L2, and 30A on L3. that would be unbalanced, and there would be current in the neutral accordingly.
Ahh yes Iv seen that on a diagram where you connect the phases using the N and have them all measured accordingly, I take it delta would only be used for distribution and we would transform to a star for buildings and such, because of the unbalanced loads we would be most certain to pull?
No, it's nothing to do with balance.
We use delta for transmission because line plant is expensive and the lowest number of wires wins. For a 3-phase system that's 3 wires.
In theory we could use 3-wire delta for distribution to individual installations and some systems work like that, without a neutral at all. Each single-phase circuit is connected between two of the three lines. E.g. one load is connected between L1 and L2, another is connected L2 to L3 etc. There's no need for the loads to be balanced, if they are unbalanced the three line currents are simply different. Shipboard domestic power is often delta, historically it was popular in parts of Europe.
But for consumers, 3-phase 3-wire delta has drawbacks. Everything has to be double-pole switched and fused because both wires of a single-phase circuit are lines. More importantly, it misses out on an important advantage of 3-phase 4-wire which is that you can take power at one voltage L-N and a different voltage L-L according to application. E.g. with 3-phase 4-wire one supply can provide 230V single-phase power with the convenience and safety of an earthed neutral, and at the same time 400V 3-phase for industrial loads with the advantage of reducing the current by sqrt(3) saving on copper and losses. These advantages of the 3-phase 4-wire system come at the cost of providing four wires instead of three, and for installations of buildings that extra cost is well justified.
So we have standardised (at least in the UK and many countries) on 3-phase 3-wire for transmission on grounds of economy, and 3-phase 4-wire for distribution to normal consumers on grounds of flexibility. Hence, most local substation transformers are wound delta-star.
I should add that there are other factors affecting the choice of star or delta connection for various applications, including how they handle harmonic currents. Because not all loads are pure resistances, even with a pure sinusoidal voltage the load current may not be sinusoidal, i.e. it may be distorted and contain harmonics. Like low-power-factor 'wattless' current, harmonic currents can add to system losses if they flow through cable resistance without delivering useful power. Because the supply impedance is non-zero, harmonic currents impress harmonic voltages on the system too, making it non-sinusoidal and possibly degrading motor performance etc.
In a 3-phase system, zero-sequence harmonics (those whose phasor does not rotate relative to the fundamental) aka triplens, 3rd, 6th etc. have the property of only flowing along the neutral, since they are in-phase in all three lines, but they can circulate around a delta winding. Therefore in a delta-star transformer, any triplen secondary current demanded by the load sets up a circulating current in the delta primary but not along the transmission lines back towards the energy source. Transmission losses and voltage distortion due to triplens are thus minimised by delta-star transformation near the point of use
this is brilliant thankyou, very comprehensive, the second part you posted I had no idea about.
Also to add something Lucian pointed out before but not mentioned in this post - the neutral is defined by the fact it is linked to earth at some point.
Traditionally that was at the substation where the star-centre was earthed, so your LV distribution was in fact 5 "wires" (3*L, N, and the E/CPC) but often the earth/CPC is the cable armour. This is TN-S
Today it is more common to have the N & E combined and earthed at multiple points, then separated at the installation, the TN-C-S system.
In Europe it is more common not to distribute the CPC, so both the transformer star and the installation have separate links to earth locally to the equipment/installation, this is TT.
But in all cases the conductor called neutral due to its low potential to earth is that way because it is deliberately linked to earth (sometimes by a current-limiting impedance though).
In Russia, there are three wires in front of the transformer on the 10 kV side, there is no neutral. There is a neutral after the transformer on the 0.4 kV side.
That is very similar to the most common UK setup for final distribution transformers with a 3-wire 11kV delta-wound primary, and a nominal 400V/230V star-wound secondary with neutral.
Others on here will know much more about the UK distribution network but I think the most common transformer size is 0.5-1MVA for urban areas, typically feeding around 100 homes.
It is rare in the UK to have domestic 3-phase supplies, though becoming more common as folk get high power electric vehicle chargers.
Reply to high voltage three wire to low voltage 4 wire? in the Electrical Engineering Chat area at ElectriciansForums.net
Extremely low voltage on 120v line Hi, I’m not an electrician but my home has 20 amp breaker that has only one outdoor outlet on it with a GFCI...
Hi everyone, When checking my consumer unit voltages with the full board off, I stumbled across something head scratching. Measuring the feed...
I am curious about voltage ratings on wire. I'm interested in 10-4 for a 25-foot cord that will be carrying 25 Amps at 240 volts. There are two...
BIG place OK lots of electrical bits. but one on a 3 phase Radial is tripping its RCCB so i check the wiring making sure its tight and it has...
Hi, I purchased a Time twin strand bell cable with a rating of 12-30V, 2A, low voltage, not for mains use. I wish to use this for installing our...
