Discuss High Ze on a TNCS system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
L
loopy
Whilst doing a Periodic Inspection on a premises that had a TNCS system i got a reading of
0.68 at the M.E.T that was four inches away.... the link between the head & M.E.T was a 16mm2 Main Earth
due to the limits being 0.35 on a TNCS system what actions should be taken... should there be a increase in the main earth to a 25mm2
plus as i always asked questions alot when i was a boy,,, why if in a TNS system 0.8 is the max then this situation would of being acceptable..
question 3 being then if all circuits still fall inside the max earth loops for the mcbs then is there a problem ... or am i from another planet ? thanku if anyone has any thoughts on this :)
I would maybe contact the DNO and ask them, as they have supplied the earthing point and it should be .35 as you know.
I dont think increasing to 25mm2 would bring the reading down that much to be honest.
Even if the circuits are well within the max allowable ZS, you still need to record and measure Ze, even on a MWC, so i would not be comfortable writing that down.
This would also make your PFC higher as well:)
Agreed.
External DNO problem there somewhere. Replacing the 16 for 25 wont make an ounce of difference over that distance.
TN-S and TN-C-S are two different beasts with a different set of parameters altogether.
Have a look here.
http://www.electriciansforums.net/r..._matters_earthing_your_questions_answered.pdf
Cheers.
Know this one from experience if you have high ze readings and zs .First thing i would do is check the main earth connection from dno main fuse to board (relavant for a tncs system )Had all the sockets off checking connections twice!turned out although looked connected was nor tightened up properly at brass connection at side of fuse .
Had this problem this week, Was getting a constant reading of 0.42 ohms on the incomer, after checking suppliers side(naughty). The installation was protected via RCD Main switch and all circuits fell within the allowed limits. I made note on my Observations sheet, Let the occupier know and sent them a covering letter explaining if full and that they should contact there Supplier and ask them to look into then matter
Did you check the PSCC ? it is extremely unusual for a TN-C-S to be this high, testing the PSCC will confirm whether there is perhaps a loose connection of the earthing conductor in the head, some of the earlier heads had internal links which had to closed by the the installation inspector on connection, if the PSCC is also high then the problem is a high impedance neutral on the network as obviously PSCC and PEFC should be the same on PME
hi can some one explain the max ze result allowed for TNCS= 0.35?
TNS=?
TT=?
and also the max loop inpedance (zs) for each system?
also what reading is good reading for r1 plus r2 and the lowest readin for IR test ?? would realy help thanks
Re: High Zs on a TT system
Hi james
if you have this high a reading on the electrode you will need to instal a much longer electrode to get into some decent soil or use a soil conditioner, what type of ground are you in and where are you measuring from, the max now for BS7671 is 200ohms
TNS=?
TT=?
The DNO`s quote 0.35 for tn-c-s
0.8 for tns
21 ohms for tt which is the supply electrode, when you add your electrode and earth conductor resistanc to this it should not exceed 200ohms for the 17th requirements
max earth loop impedance is related to the protective device operation not the particular system
r1 + r2 ? how long is a bit of string, it depends on circuit length, csa,a nd resistance per metre of the conductor
IR 1 Mohm for low voltage with a reading under 2 Mohms to be investigated when measured at the tails or bus bar
i am measuring from sockets with a new megger mft 1553 its at my house but just want to get use to the tester if u coulp help with some question it would rele help i thought max zs for a 30ma tt is 1667ohms 17th Edition Maximum Ze & Zs Values at bottom of page
right this is my readys testing from a socket!
loop = 2110 ohms
pfc= <1 A
now i dont understand pfc what reading should i be getting? the circuti is on with al earthing in place! i can not seem to get a ze reading from my megger either?
there are 2 different issues here james, THE 17TH quotes 200 ohms max is for the installation earth electrode of a TT system when measured between your earth conductor (disconnected and live, same as measuring Ze on tn systems) WARNING !if you are going to try this dont for get to turn off the ccu as you will be leaving the installation without an earth during testing, this the correct way to measure the electrode resistance when combined with rcd`s
1667 ohms is the max resistance (Zs) for a 30ma rcd/rcbo to operate within the required time to prevent a touch voltage exceeding 50V on exposed mwork etc ie 50/0.03A = 1666.66, under normal circumstances you would never expect a reading this high or indeed readily accept it
with your reading of 2100 ohms I would suspect it is the high electrode resistance otherwise you have serious circuit problems
lol well my dad wired it all up, he done the whole house been sparly for 25 yrs lol. but has no clue of regs or testin as retired.
ok so i want a min readin of 200omhs for tt (zs) what min reading for tns tn cs? sorry to keep anoyin u by asking loads of question!
what is a good pfc result?? as i am geting <1A
Ze testing = turn off supply test between L and E and N with earting disonected????
sorry have not tested for over a yr and for got every thing got essesment in 2weeks.. need all knowlege i can get
thnaks
James,
If you have your assessment coming up in 2 weeks as you say then first thing Monday go out and buy yourself a copy of Guidance Note 3, seriously it'll help you no end and has the answers to all things testing.
Have you got jobs lined up for your assessor to see, these will need completed test certification for him to see aswell.
Good luck.:)
ye i tryed to get that but no one had all whoe salers neva had one. even tryed water stones!!! im sure to get one ne way. yes i have got 2 jobd lined up one being a full wiring of a flat and other being as wiring of a garage all in pvc conduit with new CU. 2 radial sockets and 1 light. what cert do i need to show him is it the green one?
also can u please help with a pfc test ? what is good reading?
Hi James.
Sounds like you will need an Electrical Installation Certificate for each one of those jobs.
You can download certificates from the IET website or you should be able to buy them in the wholsalers i.e Robin own brand or Kewtech etc etc.
NIC will also sell you the green certificates I think you mean.
With regard to your PFC, this is in relation to your Ze as the impedance of the earth fault path will restrict the amount of fault current that will flow.
So with the Voltage of 230V and Ze of 2100 - 230/2100 = 0.11A, which isn't enough to cause your MCB/fuses to operate in the required time before the safe touch voltage of 50V is exceeded!!!! so that's why RCD protection is needed on TT system...I hope you have RCD there as you are in quite a bit of danger if not.
You really need to get the Ze (Ra) down to below 200ohms ASAP and RCD if not already present.
HTH
The max fault current is limited by the KA rating of your protective devices i.e, a Type B BS 60898 MCB is rated to a max of 6KA, BS 1361 Type 2 (suppliers fuses) are rated to a max of 33KA.
thanks lenny ur a great help!1 other thing i have for got the R2 test for lighting and ridal sockets all that is is conect live and cpc at the CU and test from socket or lighting point eg only fil in r2 test slot leave r1 and r2 blank????
Ze test is from incoming live incoming nut but with a dissconneted earth and test between live and nutral and earth bar? i done it to day got a reading of 0.18ohms and a Zs of 0.08 i think off top of my head il have a lok at test sheet?
Right, the test you have described there IS the R1+R2 test i.e linking line and CPC at CU and testing at extremity of the circuit.
The R2 test is the "long lead" test whereby you connect one end of the lead to the CPC at the CU and test betwen the other end of the lead and CPC at the extremity of the circuit.
Ze is measured by turniing off all breakers RCD's and main switches, disconnecting the main earthing conductor from the earthing terminal/bar and testing between this disconnected conductor and L+N at the feed side of your main switch.
Zs is measured with all conductors re-connected, all breakers, RCD's and main switches re energised and taking a reading at the extremity of each individual circuit.
HTH.
Ps, make sure you get that copy of GN3.;)
Reply to High Ze on a TNCS system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
After conducting a recent EICR I found among other things that the Galvanised columns in the carpark area of this premises seem to be connected...
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...