Discuss High Ze on a TNCS system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
yes i will b going denmas mon morn to get one its all cuming bk to me now
r1 and r2 for final ring is crossing over cpc and live from oppisite cables.
got a diagram for u to c il put it on nw on ze
how do u do it lol
sorry can u explain?
r1=
r2=
r1+r2=
would rele help!!
r1 = end to end test of LINE conductor of a ring circuit at the CU
rn = end to end test of NEUTRAL conductor of ring circuit at the CU
r2 = end to end test of CPC of ring circuit at CU
R2 is the long lead test I mentioned earlier
R1+R2 is the linking out of LINE and CPC of a RADIAL circuit at the CU and measuring at the extremity of that radial circuit
OR
Cross connecting L1 + CPC2, and, L2 + CPC1 conductors of a RING CIRCUIT at the CU and measuring at each socket outlet on that ring circuit.
yes got it now thank u!! funny how if u dont test for a long time u forget every thing isit it even tho i got 17th 2391 and 2330 L2 L3 LOL
ONE MORE TEST I WANT TO KNOW AND IF U COULD HELP IS SHORT CIRCIT TEST? I KNOW U HAVE TO TAKE THE HIGHEST READING EITHER FROM PFC OR SHORT CUIRCIT??
PFC is the higher of the two readings of PEFC and PSCC.
PEFC is measured L-E, PSCC is measured L-N.
On a 3 phase system as a rule of thumb, the PFC is doubled as the highest fault current would be between phases.
Ok thanks lenny very helpfull o ye if any one can help with what question the assessor will ask with the answers u would give with b good
need all info i can collect
cheers every 1
the thing is not to panic my assessor was great hes there not to pick holes but to help . he asked me questions on earthing and did tests on r1 r2 on a lighting circuit and some rcd tests make sure you got all paper work ready for him good and plenty of tea good luck
paper work !
il give him bout 4 testing certs
invoices i hav gave to clients
and some quotation i have done thing is i have never done a quote all my clients just said they want me any way. have not done one in 2years. just give ruff estimate and thy say ok kl, shw them a few figuers and away i go what other paperwork will i need
i got calibration certs ect the women said i can have insurance on the eassessment day? health a nd safty? what shel i do for that ? im going to fail i no it lo
how do i start a thread i cant seem to do it ?????????l
ye isolate cu test incomer L and N for voltage make sure dead. re test ur voltage on a volatage detector carry out visual inspection , then dead teast r1 r2 and IR then i would carry out a ze test with dissconected earth then a zs test with all eartin back on and CU live. then rcd test. say i do a r1 r2 test and connect at cu then go off to test the last point shel i put cover back on even thought its dead? im going with napit! what r they like?
yes i would prove dead then lock off make sure covers on when you leave it. heard good things about napitt electricians guide to building regs is a good book got loads of info in there
well looks like i will be going shopping monday morn pop to wholesales then go water stones lol as got a massive cricket shed to rewire. thansk for the help voltman and lenny
o yea and i have not got a lock off kit or voltage proving unit ? shel i get one i no thy r exensive for what thy r!! if not how should i prove live amd dead properly ????
Whilst doing a Periodic Inspection on a premises that had a TNCS system i got a reading of
0.68 at the M.E.T that was four inches away.... the link between the head & M.E.T was a 16mm2 Main Earth
due to the limits being 0.35 on a TNCS system what actions should be taken... should there be a increase in the main earth to a 25mm2
plus as i always asked questions alot when i was a boy,,, why if in a TNS system 0.8 is the max then this situation would of being acceptable..
question 3 being then if all circuits still fall inside the max earth loops for the mcbs then is there a problem ... or am i from another planet ? thanku if anyone has any thoughts on this :)
Re high TNCS, you could try the Ze test on the neutral incomer (PEN conductor) to the main switch with the neutral disconnected and the installation islolated, this may useful for the dno as a good reading on the neutral will point to a connection problem within the service head, on the older heads there is a seperate link to be closed between neutral and earth terminals, its possible this could be loose
Reply to High Ze on a TNCS system in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Carrying out a EICR in a commercial setting. In the main intake room the DNO supply comes in and it states clearly this is a PME system. 5 years...
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
On an EICR I found a 200 amp 3ph supply, TNS earthing (which looks original) and Ze of 19 ohms. No rods. No RCDs. L1 -> N was about 0.5 ohms...
After conducting a recent EICR I found among other things that the Galvanised columns in the carpark area of this premises seem to be connected...
So a quick catch up so you can get an idea… I was asked to do a job for another electrician, as he is too busy. I’m busy myself but said I’d...