Hi chaps.

On some remedial works at a school, I have a sub main a 16mm armoured feeding it about 50m away from the main DB. Fed from a C63 triple pole 60898.
The issue I have is the Zs at this submain is 0.46 which is way over the maximum permitted.
But the Ze at the main DB is 0.35. On a tncs btw, which I feel maybe too high also.
How can we bring this down? Or can this be noted down on the test sheets that the Ze is high hence the high Zs reading?

Thanks
 
What do you mean you have done everything to lower the values? Either installing a larger earth cable to the submain or swapping the OCPD will ensure it complies.
 
Already has the supplementary bonding, I was considering changing the mcb to a B63 but surely that will trip before the Ctype breakers in the submain DB? Will it not?
 
As the Zs is high for a TNCS could the DNO be contacted for investigations prior to any calcs and changes. They may have a take on it and be able to sort from their upstream side.
 
In this scenario you have two options.

1. To encase the complete cable run in material that will contain any fire risk that may occur from the OCPD not tripping in time.

2. To install RCD protection to the cable as RCDs have far higher maximum permitted Zs values.

The first option is not really an option due to cost so this only leaves the second option. A 500mA RCD has a max permitted Zs of 100 ohms so I would advise installing one of these at the supply end of the cable.

If you are doing an EICR I would code it as a C2 if there is currently no RCD protection on the cable.
 
The OP worded the question as though the works had been carried out, its now a lot clearer what has happened. Given that they say the max Ze of a TN-C-S can be 0.35 it has been badly designed from the start.

I agree it has been badly designed. That said the Ze may not have always been 0.35.
 
In this scenario you have two options.

1. To encase the complete cable run in material that will contain any fire risk that may occur from the OCPD not tripping in time.

2. To install RCD protection to the cable as RCDs have far higher maximum permitted Zs values.

The first option is not really an option due to cost so this only leaves the second option. A 500mA RCD has a max permitted Zs of 100 ohms so I would advise installing one of these at the supply end of the cable.

If you are doing an EICR I would code it as a C2 if there is currently no RCD protection on the cable.

Funnily enough it is in metal trunk all the way to the DB.
Think I’ll speak to my QS about the RCD option.

Many thanks for the advice.
 
Funnily enough it is in metal trunk all the way to the DB.
Think I’ll speak to my QS about the RCD option.

Many thanks for the advice.

It would need to be isolated from other cables so in its own trunking. You would also need to consider down time of supply. Personally I would stay away from this option and install a 500mA RCD.
 
Another option would be to change the OCPD from a 60898 to a BS88. BS88 would have a max permitted Zs of 0.66 ohms. Feeding DBs from DBs is never a good idea.

This is assuming there is access to a bus bar chamber though.
 

Reply to High Zs on submains and high Ze in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K
I am helping a local football club who are having some issues with Zs being too high on the submain. They have the supply Henley blocked into a...
Replies
9
Views
2K
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K
an eicr was carried out to an industrial plant area were the zs readings were all high readings above the maximum for a tns installation i...
Replies
9
Views
2K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock