Hi, can anyone help?
I've recently carried out a PIR on a school building which has 1 main distribution board supplying 9 other distribution boards around the school. Most of the installation is fine except for a number of circuits which have higher than normal Zs readings according to the given tables.
Each D.B. has BS EN 60898 mcb's and are mostly type c. There are no RCDs throughout the whole installation and most of these circuits are supplying just sockets and lights.
Is there anything I can do to overcome this such as putting type B mcbs in which would make the acceptable readings higher or fitting RCDs to these circuits?
Many thanks.
 
Rory, have you established why they are too high?

Is the R1+R2 from each sub board ok?

is the Ze on the main board ok?

or is it the R1+R2 of the sub-mains that is causing the problem?
 

Reply to High Zs readings in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

I have been asked to provide a quote for a supply to an toilet block on a campsite. The three phase supply to the campsite is approx. 150m from...
Replies
8
Views
453
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi All New to this forum, have read the posts on here from google but only recently signed up. I'm having some issues and some input would be...
Replies
13
Views
1K
all currently working towards my 2391 c&g I&T . I know how to calculate v.d. but the mock test I found online seems a bit out of date or I'm...
Replies
2
Views
702
Doing a lot of EICRs at the moment and have came across what I'm sure is a common enough problem. In an off grid rural cottage I have a TT system...
Replies
20
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock