Hi,

I am upgrading one of the electric showers in my house from 8.5kW to 10.8kW and I want to check weather a higher rated RCD should be installed.

I currently have 2x 8.5kW showers, both connected with 10mm^2 cable and 40A MCB's and a single 80A/30mA Contactum RCD (B8003/2) in my Contactum consumer unit.

I have purchased a new 50A MCB, which I will use to replace the MCB for the new 10.8kW shower, but I am now concerned that the current rating of the RCD could be exceeded if both showers are used simultaneously. Should I also upgrade the RCD (eg to a Contactum 100A/30mA B10003/2)?

Any advice gratefully received.

Phil
 
i would be inclined to leave it in but monitor it for signs of overloading. though why anyone in their right mind would want 10.8kW showers is beyond me.
 
i would be inclined to leave it in but monitor it for signs of overloading. though why anyone in their right mind would want 10.8kW showers is beyond me.


One up on the Jones next door maybe!! lol!!

I'm using a 4.2KW (maybe 4.7kw) over here and that provides pretty hot enough water, even on the coldest mornings. I don't know where they get these ridiculous KW ratings from. I often wonder if these units actually draw that sort of load, ....or if it just looks good on the box!! lol!!
 
Well the current shower (Triton) is struggling to produce a decent flow on cold mornings, so upgrading the power rating should produce a better flow.
 
the flow of water will be directly proportionate to your mains pressure, if you have rubbish water pressure then even 100kw shower isnt going to help you there

- - - Updated - - -

or do you mean a flow of hot water
 
I think the water pressure is fine. It's an electric shower not power shower, so only cold water feed. The flow rate through the shower is ok if I turn the shower temperature down, and it is especially poor on cold days since the water has to be heated more. A higher power shower should heat the water more quickly and the output flow rate vs temperature rise is better according to the specs.
 

Reply to Higher current RCD required? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I am changing the electric shower in a bathroom refurbishment (my own) and just wanted to ask about the mcb rating. The existing shower was...
Replies
2
Views
711
Hi all, I am at odds on whether RCD protection is required on an SWA of 14 metres, clipped direct under flooring direct from CU to an exterior...
Replies
9
Views
686
Hello All, I am a homeowner (but not an electrician) and I am renovating a house that has an old CU containing MCBs and an MK LN5725 residual...
Replies
5
Views
677
Hi, We are renting and have a electric shower downstairs (extension) - a 9.5kW Triton T80Z fast-fit electric shower as well as a combi boiler...
Replies
34
Views
4K
Hello Need to replace a distribution board in the next few weeks to allow for more circuits to be installed in January. Existing is a TT system...
Replies
6
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock