Discuss Higher rn than r1 in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Dartlec

Esteemed
Arms
Reaction score
2,441
Where is the point at which a higher (but continuous) conductor reading should be considered 'OK' on an EICR?

I know the theory is that it should be between 0.05 ohms, but when it falls outside that, how do others decide when it becomes an issue that must be resolved?

Checking a small flat today, with a single socket circuit - about 14 sockets in total.

r1: 0.7 Rn: 0.84 r2: 1.17

Of course the ideal answer would be to drop every socket and check connections etc...and perhaps do an r1+rn at every socket to try to isolate the issue. This flat is empty so it's probably doable, but in a normal inhabited home it becomes trickier...

Not to mention that unless you FI and then quote for the work you risk not doing much...

The same applies to cpcs where the reading is higher than it should be, but still continuous (And not just because it's 2.5/1.0 cable)...

Is there a rule of thumb people have for when they would accept it without comment, note it but not code it, or FI/C2 it?
 
Where is the point at which a higher (but continuous) conductor reading should be considered 'OK' on an EICR?

I know the theory is that it should be between 0.05 ohms, but when it falls outside that, how do others decide when it becomes an issue that must be resolved?

Checking a small flat today, with a single socket circuit - about 14 sockets in total.

r1: 0.7 Rn: 0.84 r2: 1.17

Of course the ideal answer would be to drop every socket and check connections etc...and perhaps do an r1+rn at every socket to try to isolate the issue. This flat is empty so it's probably doable, but in a normal inhabited home it becomes trickier...

Not to mention that unless you FI and then quote for the work you risk not doing much...

The same applies to cpcs where the reading is higher than it should be, but still continuous (And not just because it's 2.5/1.0 cable)...

Is there a rule of thumb people have for when they would accept it without comment, note it but not code it, or FI/C2 it?
I would use 0.05 ohms as the threshold, any higher than this would be a C2. Not a FI IMO - we can be fairly certain that, in this case, it's a loose connection which won't get better on it's own.

To fault find, I would link L+N+E on one leg only at the board, and test and record continuity of L-E, and N-E at each socket, using a socket adaptor. The L-E reading is your reference, it will tell you the position of the socket relative to the start of the leg. The N-E reading should be identical to the L-E reading up until the point of the loose connection, after which it will be higher.

This way, you can fairly quickly narrow it down to 2 sockets before having to remove any.
 
An absolute figure is hard to apply as it all depends on the size of a circuit.

Without the original EIC, you have no baseline, all three readings could be high.

Maybe a percentage of the difference between the lowest and highest?

The smallest ring I ever saw was immeasurable as the single socket it fed was right next to the CU.

Could only imagine the spark responsible had only a 32A RCBO left?
 
If you've narrowed it down to a couple of sockets or area of the house, sometimes wiggling a plug in each suspect socket while measuring rN can give it away, as rN jumps about. Not the most scientific, but I've done this successfully when the socket are difficult to remove, e.g. grouted in or minimal access.
 

Reply to Higher rn than r1 in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Morning All I recently completed my first re wire and board change, (with help from the owner who is a gas fitter and plumper, who works with my...
Replies
0
Views
1K
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Afternoon all. Bear with me on this one... Despite having been involved in the electrical industry for many years, I'm only just about to embark...
Replies
15
Views
2K
My main tester is a Megger MFT1711, which I bought second hand but came with a calibration certificate. Rather than annual calibration, I have a...
Replies
4
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock