In a building that is in the process of being converted into an hmo (11 flats) does the fire detection system need to be interconnected through each flat or just the common areas with standard smoke detectors in each flat
 
For HMO properties, the minimum cited requirement is for an LD3 system.

There are loads of guides out there that can help with this.

"For one or two storey HMOs where the individual floor area is no more than 200sqm, a Grade D, category LD3 smoke alarm system should be installed. Grade D refers to mains powered smoke and heat alarms with a built-in back up battery power supply, and the alarms can be interconnected either by wire or by radio signal. That means that fire alarm panels are not required. Ei Electronics and Kidde offer both RF and wired mains powered alarm systems as well as a range of accessories that can help you to test, locate and hush alarms easily.

Category LD3 (level of coverage) is the minimum requirement and defines where alarms should be installed. LD3 requires smoke alarms in all circulation spaces that form part of the escape routes from the dwelling, i.e. hallways and landings. If justified during a fire risk assessment, the level of cover may be increased to LD2 which requires smoke or heat alarms to be installed in specified high fire risk rooms and areas. Dependent on the specifier, this can include living rooms, kitchens and possibly bedrooms.

For Grade D system it is becoming more and more acceptable (especially if retrofitted) to install radio-interlinked smoke and heat alarms with 10 year sealed batteries rather than mains powered smoke and heat alarms. This saves the cost for the electrician and systems like this can be installed very quickly. We still recommend that you ask for confirmation by building control or the relevant council department before installing these systems.

For HMOs of 3 storeys or higher, there are two options available. The first is to have Grade A fire alarm system installed throughout the building. Grade A consists of a conventional or addressable fire alarm panel, and then fire alarm detectors, call points, sounders and beacons are specified according to the layout and requirements of the property. The second option is to have a mixed system. This would comprise of Grade D, category LD3 in the individual dwellings (see above) and a separate Grade A system in the communal areas. Again, the category of cover in the individual dwellings can be upped to LD2 if needed. Both of these options have pros and cons depending on the requirements and the owner’s accessto each of the dwellings. A mixed system appears to have become the preference, as it is likely to reduce the impact of nuisance alarms from individual flats on other occupants."


As ever, consult the proper BS5839-6 standards for more information
 
In a building that is in the process of being converted into an hmo (11 flats) does the fire detection system need to be interconnected through each flat or just the common areas with standard smoke detectors in each flat
How many floors has the property got as this will affect the type of alarm needed
 
For me the fire risk assessment should state the level Of protection required for the property and you can act according to that. Ask the buildings responsible person to see the FRA.
I dont like the idea of a part 6 covering a hmo, but thats just me.
 

Reply to hmo fire detection in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I'm completely rewiring a 9 bed 3 storey HMO in Jan, The fire detection required is just some linked lithium detectors in the...
Replies
7
Views
654
I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
252
Hi all, i'm just after a definitive answer regarding a fire alarm system in a communal area/stairwell. There are call points, smoke heads &...
Replies
4
Views
568
What are peoples opinion's on this, pair of big old semi-detached houses (85 and 87) converted into apartments, dont think its a HMO although it...
Replies
1
Views
227
Good morning, I'm in the process of a partial refurbishment which will involve the present kitchen being changed into a bedroom instead and the...
Replies
3
Views
851

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock